Discuss Sub Main Issue on Condition Report! in the UK Electrical Forum area at ElectriciansForums.net

hoppy

-
Reaction score
18
Hi,

i have been to complete a condition report in a flat today and would appreciate a bit of advice.

The db was fed via a 16mm twin and earth sub main approx. 12m run, protected by the 6o amp main fuse, tncs system. Gas bonded in 10mm at main cutout, water bonded in 10mm at db.
Main earth at db is the 6mm in the twin and earth. Dual rcd db.

I have c2 the set up, but an electrician i work with is saying c3. Do you agree it is a c2.

I believe a c3 may apply if it was a tns system and the adiabatic equation was satisfied.

Also, to rectify this would running a separate 10mm earth from the cut out to the db be ok, giving a combined csa of 16mm, or would we have to run a separate 16mm earth to comply.

Just wondered what everyone's thoughts were on this?

All advice is appreciated.

Thanks

Craig
 
Hi - personally I'd put in a new 16mm and be done.
Perhaps also check the run, is it through walls < 50mm etc so may also need RCD from 522.6.203 ?
 
Last edited:
C2, the 6.0 cpc is inadequate for PME bonding purposes. There is no calculation in this case as the Adiabatic equation is not used for calculating main protective bonding which the cpc of the cable has become.
 
Hi,

i have been to complete a condition report in a flat today and would appreciate a bit of advice.

The db was fed via a 16mm twin and earth sub main approx. 12m run, protected by the 6o amp main fuse, tncs system. Gas bonded in 10mm at main cutout, water bonded in 10mm at db.
Main earth at db is the 6mm in the twin and earth. Dual rcd db.

I have c2 the set up, but an electrician i work with is saying c3. Do you agree it is a c2.

I believe a c3 may apply if it was a tns system and the adiabatic equation was satisfied.

Also, to rectify this would running a separate 10mm earth from the cut out to the db be ok, giving a combined csa of 16mm, or would we have to run a separate 16mm earth to comply.

Just wondered what everyone's thoughts were on this?

All advice is appreciated.

Thanks

Craig
My understanding is Cables ran in parallel must be the same CSA same construction and follow the same route as would be the case if you wanted to try and add the 2 cpcs together.
Both cables would have to be able to withstand the fault current.
For the sake of running a 10mm cable in you might as well run it in 16mm if that is what you are going to end up doing.
10mm combined cpc and protective conductor would be acceptable tho as it's a cpc your installing not the main earthing conductor.
 
I am counting down the seconds until some hairpin mentions Best Practice Guide.

why? what does it say?

PS I do need to go to spec savers.. thought the OP said TNS

BUT there are countless installs, in flats with this type of "issue" and some you simply can't upgrade.......
 
why? what does it say?

PS I do need to go to spec savers.. thought the OP said TNS

BUT there are countless installs, in flats with this type of "issue" and some you simply can't upgrade.......
Best practice guide is put together with contributions by industry personnel such as the niceic, napit, the IET, beama, city and guilds, EAL.
It is as it says a guide only but to totally dismiss using, I don't understand.
As always bs 7671 is the standard we follow.
 
why? what does it say?

PS I do need to go to spec savers.. thought the OP said TNS

BUT there are countless installs, in flats with this type of "issue" and some you simply can't upgrade.......
No idea what it says I was just anticipating it.
It is TN-C-S and I agree blocks of flats are a pain in this situation, just do the Report and hope no one asks for a remedial quote.
 

Reply to Sub Main Issue on Condition Report! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock