Search the forum,

Discuss Suitable RCCB replacent in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
I need to replace this old RCCB with a suitable replacement.


Currently the one installed is not tripping on test and from the test point. Changing the entire consumer unit is not financially viable for the home owner at present so I would like to change this to at least reinstate RCD protection.

Any help would be appreciated
 
Nothing else will fit but a Sq D / Schneider of that type.
It's a unique fitting to the bus bars.

Just a note, Schneider changed all the part numbers for the old Sq D stock
QO200RCDX30 will be something else now as the replacement for the clip in type is a din rail type with an adapter.
 
Last edited:
is that faulty RCD an upfront device, doubling as a main switch? if so fit a stand alone RCD (any brand) In the tails fron the meter.

a secondary concern is that you might have a N-E fault.try testing with the outgoing cables removed.
 
is that faulty RCD an upfront device, doubling as a main switch? if so fit a stand alone RCD (any brand) In the tails fron the meter.

a secondary concern is that you might have a N-E fault.try testing with the outgoing cables removed.

No its protecting only part of the installation. A split load board.

If there was a N-E fault then the rcd should do its job. If it's not tripping then the rccb is still faulty. There was a good Zs reading on the circuit and no odd voltages across N-E.

That's how I understand it...
 

Reply to Suitable RCCB replacent in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock