I need to replace this old RCCB with a suitable replacement.


Currently the one installed is not tripping on test and from the test point. Changing the entire consumer unit is not financially viable for the home owner at present so I would like to change this to at least reinstate RCD protection.

Any help would be appreciated
 
Nothing else will fit but a Sq D / Schneider of that type.
It's a unique fitting to the bus bars.

Just a note, Schneider changed all the part numbers for the old Sq D stock
QO200RCDX30 will be something else now as the replacement for the clip in type is a din rail type with an adapter.
 
Last edited:
is that faulty RCD an upfront device, doubling as a main switch? if so fit a stand alone RCD (any brand) In the tails fron the meter.

a secondary concern is that you might have a N-E fault.try testing with the outgoing cables removed.
 
is that faulty RCD an upfront device, doubling as a main switch? if so fit a stand alone RCD (any brand) In the tails fron the meter.

a secondary concern is that you might have a N-E fault.try testing with the outgoing cables removed.

No its protecting only part of the installation. A split load board.

If there was a N-E fault then the rcd should do its job. If it's not tripping then the rccb is still faulty. There was a good Zs reading on the circuit and no odd voltages across N-E.

That's how I understand it...
 
a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.
 
a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.

I'll be honest, I dont get that. Iv had rcds that wont hold in because there is a neutral to earth short.

What neutral to earth characteristics would denote an rcd tripping and an rcd not operating at all? Earthing arrangement? Extent of short circuit?
 
a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.
Had that too. A bit of head scratching went on before I realised what it was. Disconnected circuit and RCD was fine.
 
it's weird. i can't explain the science behind it, but it does sometimes occur.
 
it's weird. i can't explain the science behind it, but it does sometimes occur.


How odd, taking into account the theory behind rcds, any neutral to earth should operate the device. I cant imagine any condition where the rcd would not see an imbalance when neutral and earth are shorted in some way....

I think by process of elimination I will still try what you have suggested and rule out neutral to earth fault
 
might be on a PME system, the N-E fault could case current to flow through E to MET and as this is strapped to N at the cut-out, backfeed through N to the RCD inhibit it from tripping. only a guess mind. as for above post. if i recall, it was a dual RCD board in one case and both RCD faied to trip.
 

Reply to Suitable RCCB replacent in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
289
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
739
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock