Search the forum,

Discuss Suitable RCCB replacent in the UK Electrical Forum area at ElectriciansForums.net

a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.
 
a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.

I'll be honest, I dont get that. Iv had rcds that wont hold in because there is a neutral to earth short.

What neutral to earth characteristics would denote an rcd tripping and an rcd not operating at all? Earthing arrangement? Extent of short circuit?
 
a N-E fault on a circuit may inhibit the RCD from operating, both on testing with MFT and the test button. had it a couple of times. once was on an immersion heater cable with a nail in it. once i had dissed the cable from the board, the RCD worked perfectly. on testing the cable, it was a dead short N-E so there was no volts N-E either.
Had that too. A bit of head scratching went on before I realised what it was. Disconnected circuit and RCD was fine.
 
it's weird. i can't explain the science behind it, but it does sometimes occur.
 
it's weird. i can't explain the science behind it, but it does sometimes occur.


How odd, taking into account the theory behind rcds, any neutral to earth should operate the device. I cant imagine any condition where the rcd would not see an imbalance when neutral and earth are shorted in some way....

I think by process of elimination I will still try what you have suggested and rule out neutral to earth fault
 
might be on a PME system, the N-E fault could case current to flow through E to MET and as this is strapped to N at the cut-out, backfeed through N to the RCD inhibit it from tripping. only a guess mind. as for above post. if i recall, it was a dual RCD board in one case and both RCD faied to trip.
 

Reply to Suitable RCCB replacent in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock