Q21 list three things to check when inspecting overcurrent devices

A21 (i) correct BS and type
(ii) Correct current setting
(iii) adequate breaking capacity

Q22 list four instances where a TN-C-S System is not allowed

A22 (i) construction sites
(ii) supplies to caravans
(iii) supplies to boats etc
(iv) temporary installations

Q23 give the reason that restricts the use of a TN-C-S system on a mobile or transportable unit

A23 A TN-C-S system may only be used if the installation is continuously under the supervision of a skilled or instructed person and the suitability and effectiveness of the earthing system has been confirmed

Q24 list the information you would require for inspection and testing of a new installation

A24 (i) assessment of general characteristics, including
(ii) Maximum demand
(iii) number and type of live conductors
(iv) type of earthing
(v) Supply characteristics, for each source of supply including standby and safety sources. (give details if asked)

Q25 state the type of inspection required on a new installation and what documents require to be filled out by the person conducting the inspection and testing of a new installation

A25 (i) the type of inspection required to be carried out is an initial verification
(ii) The documents that require to filled out are,
(i) Electrical installation certificate
(ii) Schedule of inspections
(iii) Schedule of test results

Q26 list three situations where a warning notice about voltage is required

A26 (i) where the voltage exceeds 230 volts in an enclosure where it would not be expected to exceed 230
Volts
(ii) where the voltage between live parts in different enclosures which are simultaneously accessible exceeds 230 volt
(iii) where there are different nominal voltages present in the same enclosure

Q27 list the method of fault protection most likely to be used for the following

(i) 12 V halogen downlighter
(ii) Shaver socket
(iii) Domestic socket outlet circuit indoors

A27 (i) SELV
(ii) Electrical separation
(iii) Automatic disconnection of supply, protective earthing

Q28 state the maximum voltage in both a.c. and d.c. for SELV systems:-

(i) with bare live parts in normal, dry areas
(ii) in normal, dry areas where basic protection is provided
(iii) in zone 0 of bathrooms or shower rooms

A28 (i) 25 v a.c and 60 v d.c.
(ii) 50 v a.c. and 120 v d.c.
(iii) 12v a.c. and 30 v d.c.

Q29 state why it is necessary to carry out a test of prospective fault current at the main intake position of an installation

A30 a value of prospective fault current needs to be determined at all relevant places. This means where a protective device is situated. The test is made to check that the prospective fault current does not exceed the breaking capacity of the device

Q31 an insulation resistance test is to be carried out on a SELV system. State:-
A. The test voltage to be used
B. The minimum value of insulation resistance allowed by BS 7671
C. The minimum acceptable value of insulation resistance between the SELV circuit and an adjacent low voltage circuit

A31 (i) 250 MΩ
(ii) 0.5 MΩ
(iii) 1.0 MΩ
Q32 state:-
A. Two pieces of legislation applying to the activity of inspection and testing
B. The legal status of the inspector
C. The BS 7671 requirements for the inspector

A32 (i) electricity at work regulations 1989 +health and safety at work act 1974
(ii) the duty holder
(iii) competent

Q33 A. list two methods for checking the continuity of protective conductors
B. state the percentage rise expected in the resistance of a copper conductor between 20⁰C and 70⁰C

A33 A. (i) R1+R2 method
(ii) Long lead method
B. twenty percent

Q34 in the equation Zs=Ze+(R1+R2) State what each of the symbols represents

A34 Zs = Total earth fault loop impedance of the circuit
Ze = external earth fault loop impedance
R1 = the resistance of the line conductor
R2 = the resistance of the circuit protective conductor

Q35 What calculation would you use to determine prospective fault current?

A35 pfc=Uo/Ze Uo = nominal voltage Ze = external earth fault loop impedance
 
Hi

Thanks for these Bobby. Very useful.

However, there's a bit of a mix up with questions 29 & 30. I think there are some questions missing. Is it poss to re-post with them added?

Cheers a lot.
 

Reply to sum usefull stuff 2391 pt2 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
734
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
833
Good morning all I have a summer assignment that I need to have ready before the 4th of September and I have 4 tasks that I have yet to complete...
Replies
0
Views
802
Not wanting to derail the Dodgy work pictures thread but a comment was made that a fire alarm FP200 shouldn't be in trunking with 230V band 2...
Replies
10
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top