I have tried on a number of occasions to obtain the BS(EN), Type, Rated Current and Short-circuit capacity for the supplier's main fuse from the electricity supplier. This is when there is no external identification of the fuse contained in the tamper proof sealed unit.

The answer I receive from United Utilities is that they no longer store this information for domestic premises and that it requires a "survey visit" to establish the type and value of the fuse.

Besides not being able to assess the adequacy of supply for the current and proposed usage I have two questions in relation to this:-

1. Is this now the practice by other suppliers?
2. What should be quoted on Installation and Inspection Reports?

Any ideas..... please
 
Im pretty sure they are legally required to provide that information free of charge going to have a look and see if I can find it for you.


Chris
 
Page 12 of Building Regs its Section 28 of the ESQC Regs 2002.

Lim or 60/80 for reports shows you have no access


Chris
 
Last edited by a moderator:
Nice one Chris. Just looked up Section 28.

For other readers this is what it says.....

Information to be provided on request

28. A distributor shall provide, in respect of any existing or proposed consumer's installation which is connected or is to be connected to his network, to any person who can show a reasonable cause for requiring the information, a written statement of -

(a) the maximum prospective short circuit current at the supply terminals;

(b) for low voltage connections, the maximum earth loop impedance of the earth fault path outside the installation;

(c) the type and rating of the distributor's protective device or devices nearest to the supply terminals;

(d) the type of earthing system applicable to the connection; and

(e) the information specified in regulation 27(1),

which apply, or will apply, to that installation.
 
I have contacted the electrical safety council regarding this matter ,Most of the newr cutouts are labled but are always 100 amp 1361 type 2 and they are as youd expect sealed ,so what i do on this occasion is to mark down whats written on the fuse carrier and in the box limitation " supply fuse as labled no seals have been broken " i know dam well its more than likly a 60 or 80 amp very rare a 100 amp ,i imformed the ESC and advised that electrical suppliers label the fuse, capacity and type as whats been installed in the fuse, well at the end of the day if we dont its a mark against us !! oh not heard a sausage from the ESC
 
I've had the same replies from DNO so I tell that if I dont get an answer within 7 days Ill pull the service cut out and if they don't I do
 
Just cut the seal,sorry just pull the fuse which had no sea,l and all is revealed

The amount of cut out fuses that are unsealed beggars belief

I have never been in a situation where I didn't know the fuse rating
I must be very lucky compared to some of you
 
I got this reply from ECA

1. - I am not aware of this practice in other areas, but I must say that the suppliers seem to be doing as they please at the moment.
2. - If you cannot identify the actual rating, then you should estimate the rating and record that is what has been done, and the reason.

So it seems we now have to assume that the cut-out is suitable for the present usage of the circuits..... if it hasn't blown so far... But if you were expanding the installation with heavier requirements you would need to force a visit by supplier (at their expense) to establish the rating and capacity before making any alterations.

Thanks everyone a very useful discussion.
 
I agree with Des, I've always cut the seals and opened to fuse holders to see what fuse is inside. Can't see any reason why you shouldn't be doing it. Alot of new meters have a built in isolator with a seal on and a sticker that says something like "this seal should be cut by competant electricians only" so the way I see it is if we're ok to cut that seal and isolate the supply, we're ok to do the same with the fuses.
 

Reply to Supplier's Main Fuse ID in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top