Hi all,

I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply.
What would be the best option for distribution power to each flat? I was thinking of 3 ryefield boards on 4th, 2nd and ground floor, however it will require 5x185mm SWA to run to each ryefield, optionally 3x185mm SWA and supply each ryefield as single phase (?).

It might be silly question but until now we did only max 2 storey buildings and all flats were supply from 1 location and max supply was 3 x 200A, here is my next question comes. Until now we only connect ryfield board, which maximum CSA cable for termination was 120mm, how to terminate 185mm cable then ?

Many thanks for help.
 
You can get clamp adaptors up to 240mm (I think). But have you considered doing parallel runs of smaller csa instead of having to wrestle with 185mm?
 
Are you sure on your cable sizing? 185mm seems a little oversized at first glance, especially for the lower floors.

To keep things logical you could install 1 ryefield board per floor. This would reduce the size of cable required to a more manageable level and reduce the impact of any fault which may occur on one of those submains.
 
Are you sure on your cable sizing? 185mm seems a little oversized at first glance, especially for the lower floors.

To keep things logical you could install 1 ryefield board per floor. This would reduce the size of cable required to a more manageable level and reduce the impact of any fault which may occur on one of those submains.
I'd not really looked at that - my guess would be 10 flats per floor on 60A each, so you've basically got a theoretical max of 200A /ph on each sub main - ergo you'd have a stream of 430 DNO > 400A BNO > 5no ( 200 > 60 ) in which case 185mm does seem a bit keen unless there's issues of distance and vd?
 
Just something else - Ryefield boards have a PEN connector/enabler so you might also consider whether you need to run 5c or 4c (making an assumption that this installation is an official BNO setup).
 

Reply to Supply for 50 flats in 5 storey block of flats in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi Guys, We are undertaking a large development and just want to get some ideas on how others would supply each unit. There will be a rising...
Replies
7
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock