Main protective bonds are required in this building (see Regulation 411.3.1.2) and the armour of your supply cable is inadequate to support PME bonding.
Last edited:
Discuss SWA as cpc to submain-Suitability, & PC's on RCD's. in the UK Electrical Forum area at ElectriciansForums.net
Can you verify that it is the same gas pipe in the main MET location? If so you can make sure it is bonded there (you really can't relay on steel work supports, etc) and the problem is dealt with.
Very true, but if it is the same metal that is already bonded to the MET then the job here is really ones of supplementary bonding, and for that the SWA armour is adequate.The problem would not be dealt with. The gas pipe, whether it is bonded in the main building or not, needs to be bonded at the point of entry to the outbuilding.
That might well prove to be the best solution by far. Probably cheaper than running in a new cable if the original was buried direct and not ducted, and it also avoids the issue of TT-ing the building (safe install of a rod needed, neutral-switching RCBOs if proper selectivity needed, danger of any control/signal cables between buildings becoming the "main bonding conductor" and going up in flames, etc)I wonder what the practicalities would be of getting an insulated section of gas pipe fitted where it enters the outbuilding, and whether this is more or less attractive than upgrading the bonding back to the origin.
Indeed, here is a case where the implications of a TN-C-S supply really make trouble for any existing installation. Of course it fails the current regulations, but I would doubt it is actually unsafe if the gas pipe is already bonded and the one and only common thing.I have a feeling it's going to be a hard sell to convince anyone that this problem needs solving too, so best of luck.
Now this is hurting my brain.If running a new cable is really out of the question then the obvious solution would be to TT the outbuilding and put in a 300mA delay RCD incomer or similar.
The risk that this argument on PME bonding it trying to alleviate is the case where the two buildings are in fact on different pipes. So of the incoming supply has an open-PEN fault and only the out building's pipe is a good earth (probably via other TN-C-S bonding elsewhere...) and thus you get all of the faulted segment's neutral current flowing along the sub-main's armour to this pipe and it overheats.Now this is hurting my brain.
At first glance you end up back where you started, just with a copper pipe instead of a CPC?
And an RCD that won't trip if the neutral currents are diverted.
I'm obviously missing something!
Strange you should mention control/signal cables. A fair few years back I was working in a metal framed warehouse where they grew of all things dandelions for their seeds to be used by chemical companies for weed killer production. They had made it TT but there was no electrode, the main protective bond to the structure provided a somewhat tenuous earth, it was all but non existent due to the concrete base. A couple of Zs tests took out the data cables connected back to the owners house as their return to earth was better than the steel structure.The risk that this argument on PME bonding it trying to alleviate is the case where the two buildings are in fact on different pipes. So of the incoming supply has an open-PEN fault and only the out building's pipe is a good earth (probably via other TN-C-S bonding elsewhere...) and thus you get all of the faulted segment's neutral current flowing along the sub-main's armour to this pipe and it overheats.
By making that out-building TT you no longer have that risk as no CPCs between them (overlooking the issue of any control/signal cables that might be present).
Now if both buildings are on the same pipe then your out-building Zdb is going to be very low as the parallel earth of the pipe is there, but you don't have any risk of high CPC currents, even if you do get high service pipe currents.