Discuss SWA cables - fly leading armour as cpc?? in the Industrial Electricians' Talk area at ElectriciansForums.net

Yes piranha nuts have four small spikes on the back of them, this cuts in to the enclosure wall and allows single handed tightening of the gland into them. This is what the tag-line of ‘they bite’ refers to on the front of the packet.
Well thanks Dave, to be honest never used them much as I'm retired, thanks again
 
Designers of piranha nut thought the same. But upon extensive testing they found they could not guarantee good earth, that’s why they now require flying lead.
As the piranha nut is much more substantial than a serrated washer, I would not use this method based on thier extensive testing.
 
Metal box - use serrated washers on each cable termination. By far the best solution. It acts as both ground connection and helps to prevent the lock ring from slacking off over time

Proper tightening will prevent it slackening off over time. Serrated washers are only partially effective for this, nordlock washers are about the only thing that really work for this.
 

Reply to SWA cables - fly leading armour as cpc?? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
528
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
889
Hi all. Could I ask some advice please regarding SWA banjo fly lead sizing. Can anyone explain what sizing or how you size the required earth...
Replies
6
Views
3K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock