sorry mate i was trying to be diplomatic, i'm new on the forum and their has been a few mistakes made in this topic.

as you may know people read on forums and look at the number of posts then beleive everything they say, which is a bad thing.

just because i've been at it for 28 years doesn't mean i know everything, you will find i'll ask some bloody stupid questions that apprentices will know but it may be something i've just taken for granted

And I agree and so do all the old timers out there. We can't be expected to know it all and we don't, it's all a learning curve.
 
I think the answer to the original question is, just use some G/W at the same csa as your line conductors. Nowt wrong with over sizing a cable.

Or, make sure your terminations to enclosure are bomd proof then have a juicy G/W to the earth bar.

Piranaha nuts are the things you need.
 
yes its a learning curve so hopefuly tonight you've learned the new name for the main earth its the 'main protective bonding conductor' the term for connecting cpc's into the earth bar is 'termination of CPC's' and that parts of a circuit which are not used but may become live under a fault condition require 'supplementory bonding' and that i don't generaly ' use the SWA armoured sheath as a CPC'
and finaly i am a pain in the ---
 
yes its a learning curve so hopefuly tonight you've learned the new name for the main earth its the 'main protective bonding conductor' the term for connecting cpc's into the earth bar is 'termination of CPC's' and that parts of a circuit which are not used but may become live under a fault condition require 'supplementory bonding' and that i don't generaly ' use the SWA armoured sheath as a CPC'
and finaly i am a pain in the ---

The fact you are still calling your main earthing conductor your main bonding conductor gives me a headache cause you fail to listen.

You are a pain the proverbial because you refuse to listen. I've been reading your other posts tonight, have a feeling we'll be seeing alot of you soon....oh the joy.
 
check your regs book page 167 544.1 amend 1 2011 - just remember it was you which said i described it wrong

and always a pleasure never a chore!
 
Does the adiabatic equation not calculate the minium CSA of a CPC for use with swa ? if so then how do i work out thes CSA of a sheet steel plate which is what all thes SWA cables are glanded into ???? I understand using that when your using a single SWA feeding a board for instance,it would be used to calculate the CSA of the armouring ,But when using the gland plate and it contains multiple cables i dont think this equation is applicable , i would have thouth it more likley to be a rule of thumb thing ????
 
yes its a learning curve so hopefuly tonight you've learned the new name for the main earth its the 'main protective bonding conductor' the term for connecting cpc's into the earth bar is 'termination of CPC's' and that parts of a circuit which are not used but may become live under a fault condition require 'supplementory bonding' and that i don't generaly ' use the SWA armoured sheath as a CPC'
and finaly i am a pain in the ---
That's not the new name for the main earth.
That's the new name for a main equipotential bonding conductor.
There's been no change to the correct terminology for the main earth, it's still called an earthing conductor
 
check your regs book page 167 544.1 amend 1 2011 - just remember it was you which said i described it wrong

and always a pleasure never a chore!

Your still wrong as that's describing a main bonding conductor, not a main earthing conductor. Again I stress two different things.
 
spin what is the name of that wire from the MET to DB on a TN S, what is the name of that green and yellow wire that comes from the grey service cut out to the DB on a TNC-S, what is the name of that wire from the sheath on a TN S supply that goes to the MET.

lets safely say i have probably got the terminology wrong, i'm here to learn and improve and i have already posted i may ask some dumb questions but you should know if i'm asking it others are thinking it.

domestic (always asume PME) main earth 16mm, bonding to services 10mm - thats not wrong so even though i may have got some fundemantal terms wrong i had to post that to confirm i do know a little and don't get my sizes wrong just terminology
 
so there you have it i got a term wrong which could've been serious, but as has been pointed out if i used it on site everyone would've corrected my poor terminology.

what about the original question way back 7 pages ago did i get that wrong is it perfectly acceptable to use a metal case as a CPC as has been described.
 
So why have you listened to Spin in two posts (no offence Spin) and not me in a whole thread? What was I not saying that wasn't getting through? As we established last night, it's fine if you don't know but don't drag out a whole thread pretending when clearly you got your terminology wrong.
I've never disputed you don't know the sizes but the problem is because you got your terminology wrong you don't know the difference between earthing and bonding. And if you do than it's not clearly shown.
 
the difference is easy to explain. bondage is being tied to the bed. earthing is being handcuffed to a metal bed bolted to the floor.

sorry lads.couln't resist.
 
543.2.2 A protective conductor may consist of one or more of the following:
(i) A single core cable (minimum CSA 2.5mm² if mechanically protected, otherwise 4mm²)
(ii) A conductor in a cable
(iii) An insulated or bare conductor in a common enclosure with insulated live conductors (appears to indicate that sleeving is not required when terminating T&E in back boxes etc.)
(iv) A fixed bare or insulated conductor
(v) A metal covering, for example, the sheath, screen or armouring of a cable
(vi) A metal conduit, metallic cable management system or other enclosure or electrically continuous support system for conductors (conduit, trunking, tray or even basket)
(vii) an extraneous-conductive-part complying with Regulation 543.2.6. (Re-bar, RSJ, water pipe or metal casing of a machine or enclosure such as the metal casing of a DB)

The descriptions in brackets are my interpretation.
 
From BS 7671 definitions....

Exposed-conductive-part. Conductive part of equipment which can be touched and which is not normally live, but which can become live when basic insulation fails.

The SWA armour is part of the electrical equipment, and so is an exposed-conductive-part. We earth exposed-conductive-parts so that if basic insulation fails enough current will flow to operate the protective device.



Extraneous-conductive-part. A conductive part liable to introduce a potential, generally Earth potential and NOT forming part of the electrical installation.

We bond extraneous-conductive-parts to exposed-conductive-parts so that in the event of a fault everything will be at roughly the same potential and so reduce the risk of electric shock if two parts were touched simultaneously.
 
Last edited by a moderator:
spin has more posts than you so obviously knows more than you - thats the score on forums isn't it?

sorry guys been away to pick up my son for the hols, i don't know how you cope with that M25

yes i know i got it wrong in my terms i distinctly remember argueing this with a lecturer when i did a 16th course, so you think i would of learned!
 

Reply to SWA Fly lead in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

RCBO fly neutral lead what should I be using and what supplier has them Pict
Replies
8
Views
354
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
963
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
492
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock