Posting a message to the forum will remove the above advertisement

  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. Electrical 2 Go - Electrical Supplier and Electrical Wholesalers

    Please visit our prime electrical forum sponsor - they have the best tools at the best prices. If you find a price better somewhere else, call them or contact them, and they may be able to beat it for you. Especially on an order of a few items.

    Dismiss Notice

Discuss SWA to Garden Outbuilding in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Giuliano Besenzi
    Offline

    Giuliano Besenzi EF Member

    Location:
    London
    Gents

    I need to run 10mm SWA to building at the end of the garden, the electrician suggests clipping it direct to the fence concrete post which are solid enough and says is permissable as digging a trench is not an option. I am concerned about the UV issue, the support element as the posts are 6ft apart.

    I have asked him could it be run in galvanised conduit as this would solve the UV and support problem but he says that he has never done this and is a waste of time.

    Could I ask you guys for your opininion on this.
    Thanks
     
    • Friendly Friendly x 1
  2. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Get A spark in to to do it for you Mate
     
    • Agree Agree x 1
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you could fix some treated 3" x 1" timber to the posts, then cleat the SWA to that.UV should not pose a problem ( if in direct sun, might discolour after a few years).
     
    • Agree Agree x 3
    • Optimistic Optimistic x 1
  4. Judd
    Offline

    Judd Regular EF Member

    Location:
    Liverpool
    Your electrician has never installed galv conduit?
     
    • Optimistic Optimistic x 1
  5. Giuliano Besenzi
    Offline

    Giuliano Besenzi EF Member

    Location:
    London
    No, he's not ever been asked to run SWA in conduit abd says there is no need.
     
  6. Giuliano Besenzi
    Offline

    Giuliano Besenzi EF Member

    Location:
    London
    I've got one its just the issue of can it be run in conduit or is this overkill. The sparks just wants to clip the SWA to the fence post.
     
    • Creative Creative x 1
  7. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Assuming the cable is 3 core the horizontal fixings should not exceed 400mm apart. Find another electrician.
     
    • Agree Agree x 4
  8. Giuliano Besenzi
    Offline

    Giuliano Besenzi EF Member

    Location:
    London
    The swa could be fixed direct to the post without the timber, just might need a few more masonary bits.
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    well he's wrong then. BS 7671 recommends a spacing of cable fixings and it's far less than 6 ft...... for 10mm SWA, I'd be spacing the cleats at somewhere about 18"or less.
     
    • Agree Agree x 2
  10. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    too saggy.
     
    • Funny Funny x 2
  12. Giuliano Besenzi
    Offline

    Giuliano Besenzi EF Member

    Location:
    London
    Yes its 3 core, I was hoping running conduit between post which are solid and concreted into the ground would solve the problem of 400 mm spacing of horizontal fixing, in conduit the cable would be supported along its entire length.
     
  13. Judd
    Offline

    Judd Regular EF Member

    Location:
    Liverpool
    Running SWA in conduit would be bizarre.
     
    • Agree Agree x 5
    • Like Like x 2
  14. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Use some heavy gauge cable tray.
     
    • Like Like x 3
    • Agree Agree x 2
  15. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Less than 18 hinches :D
     
    • Funny Funny x 1
Loading...
Similar Threads - Garden Outbuilding Forum Date
Back from gardening leave The Electricians Arms May 12, 2019
Garden ground spot installation Electrical Forum May 12, 2019

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job