Discuss SWA to Garden Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Gents

I need to run 10mm SWA to building at the end of the garden, the electrician suggests clipping it direct to the fence concrete post which are solid enough and says is permissable as digging a trench is not an option. I am concerned about the UV issue, the support element as the posts are 6ft apart.

I have asked him could it be run in galvanised conduit as this would solve the UV and support problem but he says that he has never done this and is a waste of time.

Could I ask you guys for your opininion on this.
Thanks
 
I've got one its just the issue of can it be run in conduit or is this overkill. The sparks just wants to clip the SWA to the fence post.
well he's wrong then. BS 7671 recommends a spacing of cable fixings and it's far less than 6 ft...... for 10mm SWA, I'd be spacing the cleats at somewhere about 18"or less.
 
Running SWA in conduit would be bizarre.
Yes but certainly would increase proterction against damage to the outer PVC. What I'm trying to get at is there a problem in running it in conduit. I understand now that clipping to the fence is allowed and should be clipped every 400mm horizontally.
Wot about running a catenary wire just above the ground, fixed to the concrete posts, and attaching the swa to that? :)
Not considered that, length is 22 metres. I was thinking of running just above the concrete baseboard on the fence.
 
Even using 25mm conduit and I have not looked those fence posts are too wide apart for fixing distances.
 
Wot about twin walled ducting laid at ground level, secure to each fence post?

Edit or rainwater pipe installed in a similar fashion (serious suggestion)?
 
Not sure you will pull a three core 10.0mm swa through 25mm tube over 22m.
Probably not but if its done in sections it might work, anyway its something I would need to do cos sparky wont. Thanks for all your input Westward. To summarise I think that there is nothing against running in conduit if its possible and providing the conduit is further supported between posts but the conduit is not really necessary, would you say thats about right Westward?
 

Reply to SWA to Garden Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
849
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi Gents, I am thinking about running some cables in the garden. The idea is to electrify the garden. My idea is to run some electrical cables...
Replies
10
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
770
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top