Discuss SWA vs HI Tuff in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Can someone tell me which regs apply to when to use SWA or when it's acceptable to use Hi Tuff? Common sense suggests that SWA be used whenever there's a risk of mechanical damage but my
thoughts on risk of mechanical damage changed when a gardener I know cut through a fat TV cable that was in the middle of ivy that had grown up over twenty years.
 
Personally I'd use Hituf if it was fixed to a wall, SWA if on the ground or under the ground.

As the designer it's your decision!
 
Last edited by a moderator:
I like Hi-Tuf: it's lovely to work with and easy to gland, but for some reason usually more expensive than SWA.

As Murdoch said, it's great for surface work outside.

But underground I believe it would need 'mechanical protection' to be compliant.
 

Reply to SWA vs HI Tuff in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am looking to replace an existing CU (ground floor) and put it in a new position (first floor). The existing CU is on the inside of a...
Replies
8
Views
3K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
13K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi, I'm guessing this is the right subforum for this. I'm a DIY'er who knows how to wire a plug and change a lightbulb. I often pretend I know a...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock