Discuss Swimming pool plant room machines in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
17
Hi I need to clarify some details I found on a EICR in Kingston. The house has a large indoor pool with a separate plant room for all the machinery.

The pool itself is upto present standards (12 years old) with a separate pit with all the jacuzzi pumps and lights which are inaccessible without proper tools ect.

The pump room has a consumer unit with 21 circuits for heating, pumping, thermostats, chemical, electrical valves ect.

The circuits all tested within norms.

The original installer mentioned on a sheet there should be RCBOs present. Instead I found only 60898 TypeB.

Should all plant room machinery have RCD/RCBO protection?

Thanks

Rich
 
Circuits within the plant room are covered by BS7671 general rules and so sockets and concealed cables would need to be 30mA RCD protected.
Circuits in the zones of a swimming pool would need to be ELV, separated or 30mA RCD protected.
 
The circuits within the plant room are in metal conduit or surfaced mounted. With circuits running to the pool in underground conduit. Lighting is all ELV.
The property is TNC-S.

More of a check as the designer/installer left a data sheet stating RCBOs. I couldn't see anything in the REGs to reinforce the need for RCBOs if ELV and separation used.

Only case I can see for RCBOs are the sockets in plant room which could be used for exterior equipment.
 
Hi I need to clarify some details I found on a EICR in Kingston. The house has a large indoor pool with a separate plant room for all the machinery.

The pool itself is upto present standards (12 years old) with a separate pit with all the jacuzzi pumps and lights which are inaccessible without proper tools ect.

The pump room has a consumer unit with 21 circuits for heating, pumping, thermostats, chemical, electrical valves ect.

The circuits all tested within norms.

The original installer mentioned on a sheet there should be RCBOs present. Instead I found only 60898 TypeB.

Should all plant room machinery have RCD/RCBO protection?

Thanks

Rich

It depends on what was installed and when. 12 years ago it would have fallen under the first version of the 17th edition, as this was introduced in 2008. I've slept since then and can't remember what needed RCD's and what didn't, but it would be worth you having a look and finding out.

In any case you need to be advising C3 for RCD's on all this kit in my opinion on your EICR, but you are the man on the ground, so its your call once you have the facts.

Cheers..............Howard
 

Reply to Swimming pool plant room machines in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Looking for some tips on supplying my pool equipment (2kw heater, 1hp pump, 1.6kw swim jet, 12w led light) with power. My house has a...
Replies
3
Views
1K
Hi guys, I've installed a new c/u for a swimming pool plant room (very small) consisting of circuits for a pump, electrics heater, pool and...
Replies
12
Views
2K
Can I pick your collective brains please for a slightly odd situation I'm struggling to find a solution for. Essentially a customer of ours has a...
Replies
5
Views
1K
S
Hello, This one is a real head scratcher and I would appreciate any help. We have installed a 4kw PV system in a field. We ran a 10mm 3...
Replies
18
Views
4K
J
Hi all Going to look at a job on monday which is to put the power into the plant room for a friend of mine who is building a indoor swimming...
Replies
3
Views
3K
eskimo39
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock