I'm the one who's spotted the faults (they wouldn't have a clue) and am trying to convince them to get it sorted. My mum's a big fan of BBC Rogue Traders so it shouldn't be too hard.

Their new kitchen was from Wickes and installed by one of their sub contractors, so they shouldn't have too much trouble trouble if they complain to Wickes directly.

I'm really miffed about a couple of things really, 1. that the ----ers pushed them into having the perfectly good 16th ed board replaced and 2. the standard of workmanship was crap anyway.

Being a non-apprentice installer, I hate the way we're portrayed and viewed by some of the JIB card holders, but it's bell-ends like this guy who give them even more fuel for the fire!
 
I'd be asking about why they felt the need to replace a 16th CU that could quite easily (I assume) had an RCBO fitted

Board was a fairly standard Wylex with single RCD, installed about 15 years ago. Can't see how they'd have had any trouble picking up an MCB or RCBO for it.
 
I'm the one who's spotted the faults (they wouldn't have a clue) and am trying to convince them to get it sorted. My mum's a big fan of BBC Rogue Traders so it shouldn't be too hard.

Their new kitchen was from Wickes and installed by one of their sub contractors, so they shouldn't have too much trouble trouble if they complain to Wickes directly.

I'm really miffed about a couple of things really, 1. that the ----ers pushed them into having the perfectly good 16th ed board replaced and 2. the standard of workmanship was crap anyway.

Being a non-apprentice installer, I hate the way we're portrayed and viewed by some of the JIB card holders, but it's bell-ends like this guy who give them even more fuel for the fire!

How has he bypassed RCD for hob ?
 
Last edited by a moderator:
I'm not sure if it's a high integrity board or not.

Out of interest, what would be the benefit of running the hob on a high integrity circuit rather than just having it on an RCD? I thought high integrity was just for safety critical circuits (fire alarms, medical kit etc)
 
If he used a dual RCD board then leaving the hob of the RCD is more difficult than connecting it properly, reason I said hi integ was he could connect onto third neutral bar this way thus removing RCD protection.
 
Non RCD circuits can be for anything you want them to be.

On all my flexible dual RCD CUs I always split the circuit between the 2 RCDs and however many spare way are left get put off the main switch. I then hope that next time a new circuit is added they use an RCBO, I hate the use of dual RCDs covering your circuits
 
A couple of months ago my parents had a new kitchen installed. Part of the install involved a new induction hob which meant a new circuit to be added to the board.

Now unfortunately they didn't tell me about anything that was going on, and ended up being talked into having their perfectly good 16th edition board replaced, instead of just sourcing an appropriate MCB or RCBO and connecting the hob circuit to the spare way.

I popped round today and whilst there I thought I'd fix a lightswitch that had been wired backwards for years. Simple enough job (despite half the screws being missing and a couple of wires simply resting against the terminals)

Few things I noticed about their new DB that cause me concern so I'd like another opinion:

- Notices missing from board (no sticker about the non-standard colours, no inspection due sticker, no sticker about testing RCD)
- MCBs labelled incorrectly (house is a little odd in that the 2 RFCs cover each side of the house, rather than upstairs and down, but not labelled as such)
- Both lighting circuits on same RCD
- Hob wired in buried T+E but not protected by RCD at all

Correct me if I'm wrong but none of the above are acceptable for a newly installed board are they? It all got me thinking about the whole installation and I'm now a little suspicious about how the initial testing could have been passed, given the fact that at least one lighting circuit clearly had poor connections in a switch.

Unfortunately I've not yet seen the certificates for any of the above work.

What does everyone think about the above? Should I be looking at take some action against this installer?
well i`d give lack of identification of circuits and general lack of notices/info as a (3)...that cable buried thing with no RCD..is (2)/(3)...seems like its mainly a requires improvement thing here.....but it is crap really....you install to the edition in place at the time....not the case here by the sounds of it.......kitchen fitters again maybe...trying their hand at leccy....
 
Taking action against a cowboy install

You have 2 chances of anyone giving a monkeys,they are slim and none at all

You want to hope they are not registered with Nicy,your chances would be zilch
 

Reply to Taking action against a cowboy install... in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock