A couple of months ago my parents had a new kitchen installed. Part of the install involved a new induction hob which meant a new circuit to be added to the board.

Now unfortunately they didn't tell me about anything that was going on, and ended up being talked into having their perfectly good 16th edition board replaced, instead of just sourcing an appropriate MCB or RCBO and connecting the hob circuit to the spare way.

I popped round today and whilst there I thought I'd fix a lightswitch that had been wired backwards for years. Simple enough job (despite half the screws being missing and a couple of wires simply resting against the terminals)

Few things I noticed about their new DB that cause me concern so I'd like another opinion:

- Notices missing from board (no sticker about the non-standard colours, no inspection due sticker, no sticker about testing RCD)
- MCBs labelled incorrectly (house is a little odd in that the 2 RFCs cover each side of the house, rather than upstairs and down, but not labelled as such)
- Both lighting circuits on same RCD
- Hob wired in buried T+E but not protected by RCD at all

Correct me if I'm wrong but none of the above are acceptable for a newly installed board are they? It all got me thinking about the whole installation and I'm now a little suspicious about how the initial testing could have been passed, given the fact that at least one lighting circuit clearly had poor connections in a switch.

Unfortunately I've not yet seen the certificates for any of the above work.

What does everyone think about the above? Should I be looking at take some action against this installer?
 
I'd be asking firstly for details of their CPS provider to check on whether they're registered. Then I'd be asking about why they felt the need to replace a 16th CU that could quite easily (I assume) had an RCBO fitted, then the stickers, then the testing etc etc. I'd then invite them to come back and test properly and certify and if they don't it's over to Dom Littlewood with them.
 
If no ones hurt or dead your complaint will likely fall on deaf ears
take up your questions and concerns with the installer first and see what he has to say for himself

Sounds like just another case of an inexperienced sparky thinking hes doing the right thing with a little bit of knowledge

Probably not intentionally trying to rip you off but he's only seen a 17th edition board in the wooden bay at the college he was working in the week before he was doing your kitchen! Lol
 
Last edited by a moderator:
New posts

Reply to Taking action against a cowboy install... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
790
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
774
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
870
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
328

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock