Discuss Testing a DIY built installation. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,021
I've been asked to PAT a tortoise house. Basically a glorified rabbit hutch.
I've had a quick look at it, but i'm not keen on getting the tester out its box just yet.

The electrical part of it, built up by the builder(? assembler? erector?), is a 13A plugtop, white 3 core flex into an IP66 box mounted on the back of the house/hutch.
Inside this is a 2 channel heating programmer. From there, the flex goes inside to a 1 gang 13A socket, and a IP rated 600mm fluo fitting.
The controller times when the light and the socket are powered, individually.

The socket then feeds a shop bought light fitting with a 75W heat lamp in it. (2 core flex)

I've told the builder the socket would need to be IP rated as well, and change the main plugtop fuse to a 3A
Apart from that, wooden structure... nothing to earth.
 

Reply to Testing a DIY built installation. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
553
Hi guys, I'd appreciate the opportunity to pick your brains a bit, and make sure I'm on the right track, please. (Will also be talking to my...
Replies
3
Views
2K
J
Hi everyone, hope you're well on this dull Sunday afternoon :) I want to add an outdoor socket for the garden and was hoping to use an existing...
Replies
9
Views
5K
Looking for some advice on what I've discovered is the electrics situation in my rental property. I'll note that before I moved in here I made...
Replies
118
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock