Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you work on/install
I dont, and I've never known a sparky who does
Feel free to accuse me of being a cowboy but here are the things I do different...

If im IR testing an old install and I get, say 50Mohms across the main Neutral/Phase and earth bars I'll write down every circuit as >200 rather than rip the fuseboard apart trying to find the circuit/circuits with less than 200. It doesn't really acheive anything IMO and takes time..
I never IR 500volts between L and N on an existing installation if the reading to earth is good, the risk of damaging the clients property is too great IMO

If im testing a new ring circuit installed by myself I'll test end to end on all 3 conductors but won't carry out cross connected ring continuity tests. On my own circuit I know its wired as a ring so this test is completely pointless.

On my own installations, if I know the chances of parallel paths etc are zero I sometimes gain my R1+R2 reading for a radial by testing Zs at the furthest point and deducting Ze. IMO this proves beyond all doubt you have a good R2. Now I know you're supposed to prove the circuits are compliant before energizing but we're all trying to make a living here and whats the worst that can happen when you know you do good connections every time and its all RCD'd

Also when I do a consumer unit change I do not test and inspect the installation to the same extent as I would an EICR. I just test ring end to end, IR L/N-E, RCD time, Ze and Zs at the end of each circuit-The going rate for C/U's (£350) does not really allow for a whole day of testing and inspection and the house is gonna be 10 times safer than before I turned up anyway.

Hopefully this should arouse some fiery debate
Seems a bit of a case of common sense vs blindly following the rules you've been given without questioning the neccessity....
 
Oh and safe isolation...I wrap the live core round me volt stick and keep turning of breakers till the beeping stops.
I also work live from time to time
 
sorry my friend but the way u sound some1 will end up in hospital,
Yeah maybe me but I'm cool with that, I like to live life on the edge....nothing beats the adrenaline rush of changing a lightswitch faceplate live....
On a serious note please describe to me a realistic situation in which anything I've described would lead to someone (other than me) ending up in hospital....
 
Why would you have to start ripping circuits apart if you had 50M ohms when Ins Res testing at the CU?

Makes it sound like you ain't much of a clue about what you're on about.
 
You just said i do not do the full test,to me i think its wrong accident can happene later, after you leave the house when dave the builder come back home to have a shower..... then you said you make up the reading from 50ohms to 200 ohms.my q to you why not do the full test and put the true reading
 
My advise to anyone thinking of working live is dont do it,especially if its not necessary

Its a shame I dont follow that advise :blush5:
I would be scared witless by someone who never works live actually doing so

Historically,electricians work has always had working live as part and parcel of the job,it is such a big no no,because of the H+S culture that is now so much more evident than years gone by

I have the highest respect for the danger of electric shock, but it doesn't frighten me one little bit,
 
If you get a reading of 50Mohms when doing the global IR test then why not write 50Mohms in the box on the sheet? Its a pass! falsifying figures as you are is (a) wrong and (b) completely pointless in the circumstances above!
 
I go all the way baby, or as far a practicably possible. No point carrying out an EICR or initial verification if you only do half a job.

Personally I think your just trolling the forum for a response...
 
Dave 85 , i knew you would get a right good flaming for your honesty lol.

Working live ? occasionally if needs must - most old skool sparks wont flinch at doing it if they have to , younger sparks have been brought up in a elf & safety bubble where even craft-knives are banned at college so are unlikely to try it.

As for testing , i tailor / adjust my inspection proceedure according to each job using methods that work for me - couldnt care less how others may do things to be honest.

Keep riding that mule Dave and i'll see you in the saloon - mines a whisky.
 
Last edited by a moderator:
If you get a reading of 50Mohms when doing the global IR test then why not write 50Mohms in the box on the sheet? Its a pass! falsifying figures as you are is (a) wrong and (b) completely pointless in the circumstances above!
Surely if I put a reading of 50Mohms for every circuit I am falsifying the figures? Either way I dont really see what difference it makes, the fact is, the IR is massively higher than the minimum requirement and theres a good chance, that the 50Mohms is spread across several circuits all of which would show >200 or very close, tested individually. Now If I got a gobal reading of 2M ohms, obviously I'd track it down to the individual circuit
 
Last edited by a moderator:
Biff,be warned when I'm at the bus Bar I always keep one hand in my pocket,(if you know what I mean,) :yes: I guarantee these newer types wouldn't understand the inuendo :grin:
 
Why would you have to start ripping circuits apart if you had 50M ohms when Ins Res testing at the CU?

Makes it sound like you ain't much of a clue about what you're on about.
If I wanted to track the 50M ohms down to a specific circuit, just so I could put 50 in the IR box next to that circuit on the cert, I'd have to pull all the neutrals outta the bar. Not always easy in an old board. If you are suggesting I put 50 next to every circuit, well, maybe you have a point.
 
As biff says i'm old school and working live has never bothered me much but have a healthy respect when doing it!

IR test L-N can be a pain. Changed a board the other day, unplugged everything and a reading of 0.02MOhms asked customer if anything still plugged in, "don't think so" but you know there is. Or it could be that you would have to pull out washing machine, dishwasher, fridge, freezer to gain access to plugs with the danger of ripping cushion flooring. I have also found the loft light is plugged in to a socket and left on. So in this circumstance if the L-E, N-E is a good reading i would probably put down 50% less than the other 2 readings for L-N. Not ideal but life isn't perfect either.
 
if you get 50 meg. on a global IR test the put > 50meg. for each circuit . ssimplessss.
 
Funny how none of the people accusing me of being cowboy/danger to the general public etc can actually give an example of how something I have suggested could possibly be dangerous (to anyone other than myself).....
I'd hazard a guess that a few (not all) of them dont really understand what it is they're doing when working and are compelled to blindly follow everything they are told in order to compensate for this lack of understanding. Probably a good thing too.

Who was it that said something to the effect of...."Rules are to be followed by the ignorant and used as guidance by everybody else"?

- - - Updated - - -

if you get 50 meg. on a global IR test the put > 50meg. for each circuit . ssimplessss.
Cheers Tel, will do this in future. Never really occured to me....
 
anthony king i am going to hazard a guess that youve not done a great deal of real life testing. this man is probably a lot more experienced than you . so have some respect . what dave says is 50ohms across the whole install . you may even find that on a large enough install, every circuit is >200 individually tested, but if you test at the tails it will be reduced as it dissipates across the large area. numpty. you dont know the ways of the spark, so LLLEEEEAAAVVVEEE IT YEAH?
 
back in the days before these new-fangled al singing, all dancing digital MFTs, > 10Meg. was the norm.
 
My advise to anyone thinking of working live is dont do it,especially if its not necessary

Its a shame I dont follow that advise :blush5:
I would be scared witless by someone who never works live actually doing so

Historically,electricians work has always had working live as part and parcel of the job,it is such a big no no,because of the H+S culture that is now so much more evident than years gone by

I have the highest respect for the danger of electric shock, but it doesn't frighten me one little bit,



And the good book says that "Live working should never be undertaken unless it is reasonably practical not to". Or words to that effect!

Cheers...........Howard
 
this is reality. and the install is safe. the zs is low enough to trip the breaker in the required time. to me it is more about the visual inspection , dropping 90% of sockets switches and isolators etc and making tons of observations. if nothing is tripping out the breakers well thats your IR fine isnt it? to me that is more about testing an install before energising i would always IR test everything. but if it is on and being used already, come on man use your loaf son.
 
My ELECSA assessor is pretty practical and experienced. (I should hope so) He advised me that when changing a CU to ins res all circuits at the same time, L and N bar strapped together tested to earth. If it's over 2M ohms then you know that individually they are much higher and will pass. With said example of 50Mohm then you write 50Mohm in all phase-cpc boxes, it's not false, it's what you measured albeit with all the circuits connected together. When I used handwritten test forms I'd write
L-N/CPC at the top to make it plain the L and N were strapped together when I'd done it. (more difficult with the PDF's I use now)
Agreed, L-N test is of negligible use. My assessor didn't seem to think it was important either. The risk of trashing electronic equipment far outweighs the value of the test.

I can't believe some sparkies see working live on the odd occation as such a problem, I agree they've probably had it thumped into them not to do it by the H&S ----'s. Fault finding for example is sometimes much easier live.

Well done Dave 85 for being honest and starting the discussion. We all might pick up some pointers. If you're just gonna slag people off then don't comment, it's not helpfull.
 
If you test an entire install and get an IR of 50 megs,then put on the form exactly that. I regularly do this, and write on the first circuit detail 'IR overall reading of all circuits'.....on the second circuit IR box I write the results.....been doing this for years and our NIC bloke has always been happy.....why do you have to fill in each circuit?
 
If you test an entire install and get an IR of 50 megs,then put on the form exactly that. I regularly do this, and write on the first circuit detail 'IR overall reading of all circuits'.....on the second circuit IR box I write the results.....been doing this for years and our NIC bloke has always been happy.....why do you have to fill in each circuit?

This seems to be the way to go, Ill do it in future. Guess I was worried that I'd get pulled up for not filling certs properly by my assessor.
Out of interest do you guys RCD test every circuit on a dual RCD board? I used to but now just test one circuit on each side.
 
anthony king i am going to hazard a guess that youve not done a great deal of real life testing. this man is probably a lot more experienced than you . so have some respect . what dave says is 50ohms across the whole install . you may even find that on a large enough install, every circuit is >200 individually tested, but if you test at the tails it will be reduced as it dissipates across the large area. numpty. you dont know the ways of the spark, so LLLEEEEAAAVVVEEE IT YEAH?

You never commented on dave not testing R1 + R2, your allready at the furthest point when doing zs, so it would take 2 mins more to carry this test out, and the safe isolation procedure seems to have gone out the window, actually i do a great deal of testing for a large chain of pubs, and i know that results can be hard to obtain especially when nothing is marked up at db or at any point on the circuit. Every one has to work live at some point i dont dissagree with that.
Oh and i never disagreed with the IR test or the results either.
 
Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you work on/install
I dont, and I've never known a sparky who does
Feel free to accuse me of being a cowboy but here are the things I do different...

If im IR testing an old install and I get, say 50Mohms across the main Neutral/Phase and earth bars I'll write down every circuit as >200 rather than rip the fuseboard apart trying to find the circuit/circuits with less than 200. It doesn't really acheive anything IMO and takes time..
I never IR 500volts between L and N on an existing installation if the reading to earth is good, the risk of damaging the clients property is too great IMO

If im testing a new ring circuit installed by myself I'll test end to end on all 3 conductors but won't carry out cross connected ring continuity tests. On my own circuit I know its wired as a ring so this test is completely pointless.

On my own installations, if I know the chances of parallel paths etc are zero I sometimes gain my R1+R2 reading for a radial by testing Zs at the furthest point and deducting Ze. IMO this proves beyond all doubt you have a good R2. Now I know you're supposed to prove the circuits are compliant before energizing but we're all trying to make a living here and whats the worst that can happen when you know you do good connections every time and its all RCD'd

Also when I do a consumer unit change I do not test and inspect the installation to the same extent as I would an EICR. I just test ring end to end, IR L/N-E, RCD time, Ze and Zs at the end of each circuit-The going rate for C/U's (£350) does not really allow for a whole day of testing and inspection and the house is gonna be 10 times safer than before I turned up anyway.

Hopefully this should arouse some fiery debate
Seems a bit of a case of common sense vs blindly following the rules you've been given without questioning the neccessity....

You talk common sense here. Far better this than the method i once saw when working for quite a well known local contractor and that was to fill out certs, without even leaving the office!
Kind of backfired when a customer had his sparks test his property, prior to doing some work, and found a break in a ring, despite the cert showing continuity readings, Turned out a plumber had hung a radiator over a hall socket, site sparks too lazy/stupid/irresponsible to even make the most basic of checks on second fixing and the office signed it off and made up all the readings! Seen this sort of thing done by several contractors now, all on new build domestic work. Bas***s quite often get away with it!
 
You never commented on dave not testing R1 + R2, your allready at the furthest point when doing zs, so it would take 2 mins more to carry this test out, and the safe isolation procedure seems to have gone out the window, actually i do a great deal of testing for a large chain of pubs, and i know that results can be hard to obtain especially when nothing is marked up at db or at any point on the circuit. Every one has to work live at some point i dont dissagree with that.
Oh and i never disagreed with the IR test or the results either.


You've changed your tune pal....
You not gonna accuse Mark ju, Joe berks, tonkatoy27and Biff 55 of all being cowboys for more or less confirming everything I said?
No.....
Thought not.
 
I find some people jump to the cowboy references far too quickly on here sometimes, just because someone does something different to the way they do it. My now fully qualified apprentice sometimes takles jobs completely differently from the way I would, it doesn't make him wrong, it just means his thought process is different. Spouting off to someone and calling them names without knowing them isn't very mature and doesn't contribute at all. (schoolyard bully springs to mind)
I see this forum as somewhere qualified sparkies can discuss and learn from each other. However, the DIYer trying to get us to tell him how to wire up his new bathroom lights so he can save a few quid should only be told one piece of advice. Get an electrician in.
 
I find some people jump to the cowboy references far too quickly on here sometimes, just because someone does something different to the way they do it. My now fully qualified apprentice sometimes takles jobs completely differently from the way I would, it doesn't make him wrong, it just means his thought process is different. Spouting off to someone and calling them names without knowing them isn't very mature and doesn't contribute at all. (schoolyard bully springs to mind)
I see this forum as somewhere qualified sparkies can discuss and learn from each other. However, the DIYer trying to get us to tell him how to wire up his new bathroom lights so he can save a few quid should only be told one piece of advice. Get an electrician in.
Oh Ive been called cowboy, DIY'er, Electrical Trainee, menace to society etc etc more times than I can remember on these forums. I must admit I do enjoy sitting back and watching people make idiots of themselves. Its quite easy to see how much weight someones opinion carries on these forums by viewing their profile and the people throwing these kind of accusations around usually carry very little.
 
As said above RCD test is for each RCD so one test on each is the right way surely, well this is the way i was taught. I also work live on occasions as its not possible to work dead all the time and i would consider myself a new spark having been trained and qualified in the latter end of the 16th edition. Am i scared of it NO, do i respect it YES. I have had a good belt on more than one occasion and that alone makes you respect what your doing more.

The cowboy word is thrown around too often in my opinion before all the facts are gained. Just because someone has a different way of doing things doesn't make them a cowboy and just because they did a Electrical Trainee course also doesn't make them a cowboy but, not testing at all or drive by testing = cowboy, those who just throw it in switch it on and collect the money without a care in the world.
Dave 85 you may not have be recording the info right before but, you were testing it (maybe not to the liking of everyone) and would have investigated further if it had been wrong. Whats wrong with that! Certainly no cowboy in my eyes.

rant over
chris
 
Out of interest do you guys RCD test every circuit on a dual RCD board? I used to but now just test one circuit on each side.

Do rcd tests at the board with all mcbs turned off to reduce " electronic noise " from appliances.
2 rcd CU = 2 separate tests at the device.
 
Do rcd tests at the board with all mcbs turned off to reduce " electronic noise " from appliances.
2 rcd CU = 2 separate tests at the device.

Aye bloody obvious really, I've been doing it that way a while now, Was taught at college to RCD test every circuit. Nonsense
 
i tend to test RCDs at sockets. reason is that i generally use the auto test function and it's not easy to keep probes in contact with the RCD terminals whilst resetting the RCD after each trip. also, IMO, in the real world thae RCD is expected to trip if necessary with circuits and loads connected, so why test with circuits OFF. ?
 
It's your name on the cert not anyone else's so you do what YOU think is necessary.

Shock horror I sometimes do no IR on a CU change instead I bow to the good old bang test.

However I never leave a job without being confident that it is safe.


There I was honest.
 
i tend to test RCDs at sockets. reason is that i generally use the auto test function and it's not easy to keep probes in contact with the RCD terminals whilst resetting the RCD after each trip. also, IMO, in the real world thae RCD is expected to trip if necessary with circuits and loads connected, so why test with circuits OFF. ?

I like this method too. Much easier to plug in MFT and place on floor or kitchen worktop and leave on auto test and not be trying to hold probes and reset the RCD.
 

Reply to Testing...how far do you go? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
690
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
933
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
313
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock