.......... so why test with circuits OFF. ?

The rcd manufacturers themselves recommend the testing is done off load.
Some brands are suseptable to give inaccurate readings if loads are active downstream.
In many cases it doesnt make much difference but that is the guidance given anyway.
 
Last edited by a moderator:
wow a very good honest chat i'm impressed indeed . i've always thought this site should be called to good to be true electrics .

its a weight of my mind i thought i was the only one living in reality
 
Do rcd tests at the board with all mcbs turned off to reduce " electronic noise " from appliances.
2 rcd CU = 2 separate tests at the device.


or


Switch Off all loads at their switches
Use Plug-Lead of the MFT on auto-test to test the RCD's, at the most convenient socket
 
wow a very good honest chat i'm impressed indeed . i've always thought this site should be called to good to be true electrics .

its a weight of my mind i thought i was the only one living in reality
Yes, I totally agree. It didn't start too well, I thought I was gonna get hung out to dry after the first 5 responses from incompetent illiterate fools, but the naysayers have gone suprisingly quiet since the proper sparkies who know what they are about have spoken up.
 
It's your name on the cert not anyone else's so you do what YOU think is necessary.

Shock horror I sometimes do no IR on a CU change instead I bow to the good old bang test.

However I never leave a job without being confident that it is safe.


There I was honest.


Well said!
I have to say, mind, that recently I have taken to IR testing each circuit as I go when doing a C/U change just to prevent myself tearing my hair out when I turn it on the RCD'd wont hold.

The guy I used to work for, when 17th ed boards first came out, on several occasions, replaced both rcd's with main switches after a CU change because he couldn't ever work out how to get them to hold in and fault finding was completely beyond him. Have you ever heard anything like it? Its insane.

For the record he did a full 2360 apprenticeship, AM2, 16th edition, NVQ the lot. Far more qualified and experienced than I ever was.

He went bankrupt three years ago in a year where he turned over about £150-200k with just me and an apprentice.

Proof that incompetence catches up with everyone in the end....
 
Alot of good sparks dont get their heads round testing , which is why 2391 has only 30% pass rate.
Of course i did mine back in '97 when the exams were really hard :)
 
Yes, I totally agree. It didn't start too well, I thought I was gonna get hung out to dry after the first 5 responses from incompetent illiterate fools, but the naysayers have gone suprisingly quiet since the proper sparkies who know what they are about have spoken up.

you started this thread as a wind up,as for being called a incompetent illiterate fool,Ihave worked with some right nobs
who don't give a stuff about looking out for them selfs or anybody else,so in my case because i work on forecourts & fuel storage depots with petrol/diesel, i am a little sensitive to people not working safely.
 
Interesting thread: I am from the earlier version of sparky (industrial background)
Anything new and anything i have not installed gets full 500V treatment - so does anything like a simple radial where i am confident i know exactly what the cct is and there is no chance its spured off anywhere.
Everything else gets 250V - this has saved me numerous times when i have subsequently found additional equipment.
I spend at least half my time on visuals and making sure i have found everything i can. This is no mean feat in a factory environment with so much electrical equipment fed from control panels rather than from Dbs.
RCDS tested from nearest socket with MFT on auto.
Grouped IR numbers repeated across whatever group i have done.
I usually find i have to get my hand into the board so when i have finished i generally put the DB cover back on and do Zs tested to ensure i have not put a fault on and then test the device.
I am not generally testing to a fixed price but overall i am more likely to mess up on missing a broken socket / switch/isolater etc etc that fails basic insulation of live parts as is the environment i am working in so this takes my priority. To be honest if i cannot find a circuit it goes down as "not found", if i cannot get an IR reading cos i know there is sonmething plugged in out there, it goes down as Limitation with comment. If stuff is too high to reach - ditto.
Don't do much house stuff but suspect IRs on sockets and lights could be interesting.
Much of the work i do is live, whether i am in a DB adding ccts or testing. I work as if everyhting is live and rarely get a belt (mostly off neutrals).
If i am working on lighting i am more likely to work live as i hate being in the dark so will always try and keep the lights on - TBH its no big deal and i honestly cannot see what all the fuss is about, after all its only 240V !!
 

Reply to Testing...how far do you go? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
684
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
930
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock