Discuss Testing Modular cabins on site. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

a12jpm

-
Reaction score
22
A customer has asked me to test some site cabins for him. Basically as far as I can tell it's pretty much the same as domestic stuff just a good bit smaller. Does anyone have any experience testing cabins and any pointers I should be watching out for.

I also have a price figure in mind per cabin but would welcome any guides as to what you guys are charging, I think I might be a bit cheap. I've got 13 cabins to test all on the same site.

Thanks in advance.:)
 
Hey.

Before you do anything, does your mate actually own these cabins or are they on hire??

If they are hired then dont be messing with anything internal, the hire compnies will hunt you down and shoot you dead!!!:D, you should only test the supplies to them.

What type of cabins are they? steel containers, insulated, canteens/toilets??


On the other hand if he does own them then pretty much the testing is the same...obviously everything should be on 30mA RCD, make sure everything is earthed - pipework, the cabin itself.

Make sure you have a good Zs/Ze, if they're geney fed then I always rod the geney and each cabin.If they're close together i.e touching distance then they should be bonded together also.

Sorry to go on but if they're on a construction site then they should be tested every 3 months.

Hope this helpd you out a bit.

Cheers.
 
Cheers for the informative reply Lenny, exactly the kind of stuff I was looking for.:)

I will be testing for the company that owns the cabins and hires them out. They have about 2500 units so this could be a nice one for me if I get it done right. Not all the units are out at the moment but hopefully when the economy get going again this could be a nice wee contract for me.

The cabins are steel linked together by steel frames and they are nearly always geny fed if thats any help.

Thanks again for the reply, much appreciated.

Cheers for the informative reply Lenny, exactly the kind of stuff I was looking for.:)

I will be testing for the company that owns the cabins and hires them out. They have about 2500 units so this could be a nice one for me if I get it done right. Not all the units are out at the moment but hopefully when the economy get going again this could be a nice wee contract for me.

The cabins are steel linked together by steel frames and they are nearly always geny fed if thats any help.

Can i be cheaky and ask what you charge, still trying to find my feet with this one. By all means tell me to **** off, but as they say up here nae cheek nae chance!

Thanks again for the reply, much appreciated.
 
Last edited by a moderator:
If they are hired out then it is a waste of time doing any live tests on them as when they get to site the test certificate is no use as the site they will be on will have totally different supply characteristics to where they were first tested.
 
Thanks for the replies guys.

Looks like i've got the job, wayhay!

I'm doing it on behalf of the hire company who supply the cabins and all testing is to be done on site after install and every 6 month after that, oh and while i'm there the PATesting has to be done - bonus. They are not massively busy at the moment but they reckon at least 1-2 days a week testing so this could be a steady income for me and it's been a while since i've bean able to say that.

'll let you know how I get on.
 
Right, well not one to disappoint I thought I would keep you posted. Please feel free to ignore.

Got back from a week off at Centre Parcs (or "don't forget your chequebook" as i have now christened it robbing barstewards) and I have a fax sitting from said cabin hire company -
13 cabins in near Dundee and 11 cabins near Glasgow all to be tested and PATesting done by the end of next week!

At last something seams to be going my way.
 

Reply to Testing Modular cabins on site. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

As I have retired now (really!) I have decided to sell my electrical tools etc. They include hand tools, hilmor galv. conduit bender 20/32 with...
Replies
12
Views
1K
I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
783
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock