Hi all,new to testing so go easy on me if it's a silly question,On a periodic when testing r1+r2 & zs on a lighting circuit with ELV downlighters fitted how is it done.If the transformers are not accessable:eek: for bypass or disconnection is the r1+r2 test just done up to lightswitch or would it just be agreed as a limitation not to do the above tests with the customer & noted on the test results & just do the IR test with L&N connected together & test between earth.As i said go easy as experience will come eventually:D
 
Are we getting confued with R1/R2 and insulation resistance here?

No mate,maybe i didn't explain it clearly.what i meant is i could do the IR test in the procedure i stated because the transformer cannot be disconnected but for the r1+r2 test be carried out what would be the procedure.Does that make sense to you:confused:
 
You should have an idea of when the work was carried out. The extent of the installation and limitations should have been discussed prior with the client. You test what you can get at and note this on the report.
 
I wouldn't be too concerned with r1+r2 value
If they were class 1 fittings then yes it would be important to ascertain the r1+r2
The cpc is not going to carry a fault current unless its a cable fault
I would be much more concerned that the transformers were inaccessable in the first instance
I would prefer to know that there is sufficient ventilation around them and they are not covered in the wooly stuff
Anything that is not tested should be agreed and noted as a limitation
If testing r1+r2 can only go as far as the switch then have that agreed and noted
In the end you are not there to rip the install to bits for the information
The insulation resistance test sounds reasonable to me
You should have access to the transformers for the test between the supply and the selv to test for seperation
 
If its a PIR, then you note it that the transformers were inaccessible. So you carry out the r1+r2 at the most convenient points on that circuit. Make a note that you are unable to verify connections at these transformers too. Why can't you get to the transformers ?
You are correct in doing the IR test by linking together the L and N conductors, and testing to E. Again, the L-N IR test must be noted as a limitation due to connection of equipment which could not be disconnected.
 
If its a PIR, then you note it that the transformers were inaccessible. So you carry out the r1+r2 at the most convenient points on that circuit. Make a note that you are unable to verify connections at these transformers too. Why can't you get to the transformers ?
You are correct in doing the IR test by linking together the L and N conductors, and testing to E. Again, the L-N IR test must be noted as a limitation due to connection of equipment which could not be disconnected.
Thanks this answers all my Questions so thanks for all the replies.The transformers are inaccessable because they are not behind the fittings they are somewhere under the floorboards & customer does not want carpets/floorboards ripping up & neither do i;)
 

Reply to Testing r1+r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
842
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
614
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
895

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock