Discuss Testing RCD on shower circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

This is a picture i've taken of my megger and test leads connected to do the RCD test on my mk dual RCD board

ImageShack® - Online Photo and Video Hosting

Obviously i have not put the busbar in yet but u get the drift.

Main switch on MCBs off RCD ON then test load side of RCD line to earth for that particular RCD or like not so clever pointed out if the RCD side you are testing has a circuit using socket outlets then just use the plug on the megger and test at socket outlet.
first test 1/2 then 1 then 180 wave then 5 then 180 wave record two highest results. The 1/2 test should not trip this is a test to gauge how sensitive the RCD might be ?
Then finally test the manual button on the RCD to see if it works.
 
Last edited by a moderator:
Looks fine, you do your tests right there on that RCD and the results will apply to the 4 circuits protected by that RCD.
 
yeah thanks then ill repeat the same test for the second RCD and that will take into account the 3 circuits on that RCD.
Thanks for fast reply volt.
 
personally, i just plug in to the nearest socket outlet, with loads removed. problem with using probes is breaking a connection when resetting the RCD. it's rare to find a RCD without at least 1 socket circuit on it. ( RCBOs excepted )
 
Hi,

Sorry to jump in on this one but, something i come accross the other day, old style re-wirable fuse board with a completely separate rcd for the shower, the pull cord switch went in the bathroom so i just replaced it like for like, the rcd was operating mechanically but how would i test it at the shower/pull switch? (I've disconnected it for the time being). Can i just connect the leads at the pull switch? just seems a bit unsafe doing it this way as obviously it's a live test?

Thanks

Ben
 
test at the CU. it's easier. switch off all MCBs on the RCD you are testing. clip to earth bar, probe to L on load side of RCD. ( mft set to RCDauto ). switch on RCD, press test button on MFT. reset RCD each time it trips. read off and record trip times. enter the higher of each on schedule of test results. press test button on RCD to confirm operation. ramp test if required. done.
 
Still not sure as it's on re-wireable fuse board, shower circuit doesn't even go through the main fuse board, it's located separately mounted below. I thought rcd was live test?
 
test at the CU. it's easier. switch off all MCBs on the RCD you are testing. clip to earth bar, probe to L on load side of RCD. ( mft set to RCDauto ). switch on RCD, press test button on MFT. reset RCD each time it trips. read off and record trip times. enter the higher of each on schedule of test results. press test button on RCD to confirm operation. ramp test if required. done.
Yes it is a live test just follow the above instructions easier than any manual
 
From what i can remember it looks like it was fed directly from the meter tails, 1 set goes to the main fuse board another set go into a separate RCD then onto the shower pull switch. Also whe i was taking the switch down i had a small shock off of the earth wire, is this normal? i performed an IR test between live and earth and it came back ok, not sure why there would be any current/voltage in the earth wire. I noticed something on here about earth leakage but this is a completely separate circuit for the shower, nothing to get leakage from, confused.com

Regards

Ben
 
If your getting a tingle of the earth, it could mean that the CPC is not connected somewhere or the neutral is loose somewhere.

Also if the RCD is fed direct of the tails then you don't seem to have any overload protection.
 
as you describe it, there should be a MCB alongside the RCD ( 40A? ). if not, then as malcolm says, no overload protection for the shower cable = FIRE.
 

Reply to Testing RCD on shower circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
341
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
543
I live in Australia; you can use a socket tester to test the RCD for the power outlet circuit. Plug device to a 3-pin wall socket, set testing mA...
Replies
2
Views
894
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock