she might get rid of you has well.Yes, she wouldnt let him back to do anything else. She wanted rid of him
Discuss Testing someone else’s work in the UK Electrical Forum area at ElectriciansForums.net
she might get rid of you has well.Yes, she wouldnt let him back to do anything else. She wanted rid of him
Shouldn’t be to hard to rectify them mate,does she want the eicr or just making good? If she just wants making good I’d confirm the cpc visuals at the Cu and also at the socket (I’d guess it’s come loose) couple of tests to confirm stuff and things and then as Pete says mwc,Yes, she wouldnt let him back to do anything else. She wanted rid of him
Only just seen this and tested it today and didnt take any photos, the chap had already been round to sort it out and apart from being untidy i couldnt fault it.Be interesting the see what the outcome of this is OP, can you take some pictures when you unscrew the socket. Before disconnecting/testing anything.
DiLog MFT Pete, do try and keep up.Di-log what?
Hate to bang the drum again, the ONLY thing 18th Edition is the Regs.
At the top of the screen there are 3 icons L-N
L-E and N-E, when the connection is there they go solid, they flash when there is no connection.
L-N was solid the other 2 were flashing
Tom,
If she is concerned about the safety of the work carried out, then yes, you can carry out an EICR (which, given it's a spur from what I'm assuming is a ring final circuit) should include a full suite of dead and live tests on the circuit, along with a visual inspection of the work carried out.
As the house is new, she should have access to the original EIC for the installation which you can refer to for test results for the circuit that was worked on.
Hope that helps.
Regards
SC