Discuss testing in the Australia area at ElectriciansForums.net

F

fire

two lighting circuit, one upstairs one down stairs, both on serparate rcds when i test down stairs at the last light for zs not a problem, when i upstairs at the last light, just beeps but doesnt give me a zs, why is that?
 
two lighting circuit, one upstairs one down stairs, both on serparate rcds when i test down stairs at the last light for zs not a problem, when i upstairs at the last light, just beeps but doesnt give me a zs, why is that?

Have you checked polarity? If the live is mixed with the neutral then instrument won't take a reading
 
Animal has said the first thing that comes to my mind have you measured R1R2 if you have a high continuity reading R1R2 the you could well have a loose connection some where on the circuit this could be even an open circuit , this is why the test proceedures should be followed dead test R1R2 , insulation resistance , then Zs , so redo the R1R2 and insulation tests and the rechech it could also be a fault on the lives , when you carry out a Zs test it reproduces a fault on the system and measure the resistance of the fault Ie earth fault loop impedance Zs if this is too high then the meter could bleep hope me waffling on abit helps
 

Reply to testing in the Australia area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
605
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
850
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock