Discuss Three phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi guys, I am rewiring a commercial launderette with 3 phase machinery.



Does the machinery need to be RCD protected being in commando sockets.



The sockets are not accessible to the public and each circuit is being used for a specific machine.



With the price of three phase rcbos the customer is not happy
 
Last edited by a moderator:
Yes, but if the rcbos are cost prohibitive look at the outlets you can fit rcds in (as long as your supply cables dont already need it) probably be similar costs though so hes/shes gotta swallow it, or you cut the plugs off and wire to rotary isolators, also see what manufacturers instructions say
 
3-phase RCBO are expensive and often take up extra space leading to "lost" slots in TPN boards, so you might well end up cheaper to use socket & RCD combinations as @suffolkspark suggests, or as we did for a couple of 3P A/C units to put the RCDs in a DIN box adjacent to the TPN board.

But if the equipment can be hard-wired to lockable isolators for maintenance that would be cheapest and least trouble overall.
 
Don't forget though, there are a few reasons why rcd/rcbo are required, not just because they are socket outlets, so if the wiring is less than 50mm behind the wall etc. Then the rcd function needs to be at the feed end.

Surface wiring or protected cables(armoured or conduit/trunking) would be fine with the rcd at either end.

Surface cable to fixed equipment (no socket) then no rcd required.
 
Cables will be clipped to basket surface mounted, wiring the machines to lock off rotary isolaters is possible and was my next option.

So by wiring to the isolator rcd protection will not be required.

Cables will also be armoured
 

Reply to Three phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
748
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
363
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
854
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
825
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock