Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
 
SWA shouldn't get moisture ingress unless you have damaged it during installation, why go to the trouble of putting it in pipe?
 
Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
Measure the diameter of the cable. If it's less than the alkathene then it will fit. If it isn't it won't
 
If it's there for the long haul then why not add a barrier, anything that slows down corrosion is a good thing as far as I'm concerned, what if it got a scratch in the sheath whilst laying it and the armour corroded? I don't fancy going back to it for free.
 
If it's there for the long haul then why not add a barrier, anything that slows down corrosion is a good thing as far as I'm concerned, what if it got a scratch in the sheath whilst laying it and the armour corroded? I don't fancy going back to it for free.

I agree that it's prob best to put it in a duct, due to sharps/stone in the backfill material but put it in a proper cable duct as Ruston says you wouldn't want people thinking it's a water pipe. Plus if you put it in a a proper cable duct it would be easier to replace should some one have to at any point in the future, you would have a hell of job trying to replace a SWA through a bit of 25mm poly pipe lol
 
So I carry out a sheath test which tells me the sheath has been compromised, then what? I guess I rip it up and put into some MDPE pipe? I'm more a prevention is better than cure guy TBH.
 
So I carry out a sheath test which tells me the sheath has been compromised, then what? I guess I rip it up and put into some MDPE pipe? I'm more a prevention is better than cure guy TBH.

Use Polyduct from builders merchants like Jewsons. i think it is something like 32/38mm Dia. but will do the job easily. use marker tape above it though.
 
Good point leesparkykent & ruston. Could leave a plumber in a spot of bother if he tried to tee off for a water supply haha. Mind you the yellow warning tape above should be a clue.
 
Sheath test???? What voltage and nature of the installation are we discussing here!


Not sure where or how you were trained but swa is good for direct burial and if not exposed to corrosive chemicals or mechanical hazards then will be good for many decades, there is really something wrong with your installation methods if you manage to damage the outer sheath to the extent it lets moisture through to the armour, unless your using mechanical means to back fill and compact the ground.
Is there an inherent risk of damage during or after its been buried?

Having said this ducting is commonly used where the costs of servicing, replacing the cables would be high in the event of a failure, in this case use the correct cable duct, depth, burying methods and hazard marker tape or is this for a little garden number - supply to a shed/garage.
 
Last edited:
Good point leesparkykent & ruston. Could leave a plumber in a spot of bother if he tried to tee off for a water supply haha. Mind you the yellow warning tape above should be a clue.
Generally...Black ducting is used for electric cables. U/G cables are black including DNO's mains cable. However years ago and still in use is the old plastic water pipes which are also black. So take nothing for granted. Do the job right first time
 
Sheath test???? What voltage and nature of the installation are we discussing here!

What difference does the voltage make? A sheath test should be done on any UG cable to confirm the integrity of the serving. The only exception I would make is for tarred hessian serving as it is designed to allow leakage of circulating currents.
 
Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
The 25mm dimension of polyethylene pipe usually refers to the outside diameter so internal it will be a ball-hair over 20mm. I assume you're using a 2-core in which case it'll be around 17mm dia so it's going to be a tight squeeze and probably won't be an easy pull for 15 meters but it should be possible if you pull the cable through the pipe first with a fishtape then put it in the ground afterwards. I'd personally go with a larger duct like a 40mm because I hate struggling with stuff like that and I'd plan the job for a warm day when it'll be easier to get everything rolled out nice and straight.
 
What difference does the voltage make? A sheath test should be done on any UG cable to confirm the integrity of the serving. The only exception I would make is for tarred hessian serving as it is designed to allow leakage of circulating currents.

Was questioning to lead the posts the correct way, I don't deal or have experience with HV so would be out of the conversation but if he's talking about running a 6mm 3core to his shed under his back garden then its all usually manual backfill and wouldn't warrant a sheath test as most domestic sparks don't have the appropriate tester to do so, no column on their test sheets for it either... wasn't questioning the testing of the sheath but the circumstances of the install if he's doing a sheath test as this tends to be past your domestic set ups thus curiosity got me, not often a test mentioned on here.

I bet you can drop this conversation into the forum and 90% of the guys who have buried cable on here will not have done a sheath test, I've not done it often myself but thats more to do with the fact I don't bury many cables. I questioned him because of his strange question at the beginning of using a blue pipe as a sheath - its one of them things that ring alarm bells, so had to clarify exactly what kind of install he's doing, he seems to do a test that most on this forum will never have even done yet asks a weird question to boot when standard ducting would be the way to go, even if he had a 10mm clearance he would not get that swa though that pipe as both would have natural bending in them from storage and the friction would be high over 15m length.

@OP - I wouldn't be going anything less than a 50mm duct to drag a 6mm swa through, it will also allow for future issues to be easily rectified if needed to change the cable.
 
Last edited:
Think E54 will confirm this, it’s standard practice to confirm the integrity of the outer serving a few days after the back fill has been done no matter what the system voltage is.

Most of our UG supplies relied on the armour as the earth (no CPC then) to have it corrode away could be disastrous. In reality it never would be that bad as the numerous X linked cables maintained integrity.
We used high conductivity armouring where 1 in 5 armours is tinned copper. These cables are special order, you put one at risk by poor installation methods and there would be all hell to pay.

A sheath test would be normal before the ends were connected. I don’t know what voltage E54 uses but I’ve always used 250V DC between the armours and earth.
 
We don't always sheath test SWA's but if we do we usually common together all the conductors and the sheath and run 1kV through it which is usually what their ins is rated to.
 
We don't always sheath test SWA's but if we do we usually common together all the conductors and the sheath and run 1kV through it which is usually what their ins is rated to.

The outer serving isn’t an insulator hence the lower voltage. It isn’t a standard IR test.
 
I agree that it's prob best to put it in a duct, due to sharps/stone in the backfill material but put it in a proper cable duct as Ruston says you wouldn't want people thinking it's a water pipe. Plus if you put it in a a proper cable duct it would be easier to replace should some one have to at any point in the future, you would have a hell of job trying to replace a SWA through a bit of 25mm poly pipe lol


If it has been installed correctly before you backfill the excavation the cable should be covered with a layer of sand to stop the cable being damaged by stones or sharps.
 
If it has been installed correctly before you backfill the excavation the cable should be covered with a layer of sand to stop the cable being damaged by stones or sharps.

Do it properly? Too much trouble for many. Get it in quick and hide it before Tony sees it, that’s where the sheath test came in.
Most of my work involving UG cables was in a quarry. You want sand, how many tonnes? Chatter by the wagon load if needed.
At the foundry we used granulated slag as the infill, again, how many tonnes?
 
Do it properly? Too much trouble for many. Get it in quick and hide it before Tony sees it, that’s where the sheath test came in.
Most of my work involving UG cables was in a quarry. You want sand, how many tonnes? Chatter by the wagon load if needed.
At the foundry we used granulated slag as the infill, again, how many tonnes?

Was on the way but got a dam puncture lol
 

Attachments

  • 22843-1f.jpg
    32.7 KB · Views: 72
If it isn't an insulator does that mean it must be a conductor?

(Please don't shout at me Mr Grumpy Git sir)

Smart arse! ;)

Yes it is an insulator but in the terms of electrical isolation in a cable that isn’t its function. Its function is purely to protect the armourings.

Lucian Nunnes of the Electrotechnica Museum mentioned unserved armoured cable. I’ll be honest I didn’t believe him. He posted these, I couldn’t argue then.

Unserved20PILCSWA202_zps3db23391.jpg


Unserved20PILCSWA203_zps6a8e4282.jpg


This picture shows unserved tape armoured cables. I’ve not worked on tape armoured since I was an apprentice, like everyone else I finish up with shredded finger ends. The stuff is bloody evil. When you cut it you have two barbs waiting to stab your hand and the joy of razor sharp tapes.

Unserved20PILCSWA201_zps345e86da.jpg
 
Thanks Dave. I've maintained buildings much older than that and never seen unserved cables before so it's interesting to hear about them.

Daft question, but would I be right to assume that they are only for dry areas?

The cables in Lucians photographs are acording to the information are PILC.

Most old PILC cables are first wrapped tarred paper and then a layer of tarred jute. Over this the first layer of armourings followed by another layer of tarred jute. A second layer of armourings over wrapped with tarred hessian. Just to add to the fun it would then be whitewashed to stop it sticking together on the drum.

Stripping it you set off covered in whitewash, followed by tar. The only way to clean the tar off the armours and lead sheath is with paraffin and a blowlamp. By the end of the day you were a fire hazard and reeked to high heaven.
We nearly burnt the EMEB training centre down with a bit of a cock up with the paraffin rags and blowlamp.
 
If you could Dave. You know my interest in the history of our trade.

I will do my best to remember, I think we've got a show going in there in March. The installation is a bit of a shambles at the moment though. As usual the remaining bits of the original installation are well installed etc, but the more modern abortions are a disgrace.
 
The cables in Lucians photographs are acording to the information are PILC.

Most old PILC cables are first wrapped tarred paper and then a layer of tarred jute. Over this the first layer of armourings followed by another layer of tarred jute. A second layer of armourings over wrapped with tarred hessian. Just to add to the fun it would then be whitewashed to stop it sticking together on the drum.

Stripping it you set off covered in whitewash, followed by tar. The only way to clean the tar off the armours and lead sheath is with paraffin and a blowlamp. By the end of the day you were a fire hazard and reeked to high heaven.
We nearly burnt the EMEB training centre down with a bit of a cock up with the paraffin rags and blowlamp.
Tony,

Thanks for your reply and explanation, it's interesting and much appreciated. My previous workplace had plenty of PILC with the tarred Hessian wrapping, but I've never seen them without it.

Very interesting to hear about the use of whitewash to stop the cable sticking to itself on the drum. I have to admire those people who installed the stuff.

Thanks again
 
Any SWA cable that's been installed into a buckshee trench that hasn't had the sharp stones and other debris removed from the base of the trench and then just backfilled with the excavated earth is almost certain to have it's outer sheath compromised!! There are good reasons behind how a cable trench should be constructed with the correct procedures and materials....

Basically the above is unfortunately a description of what normally applies to domestic buried cables, that are not run in a suitable duct. You would be surprised, even when direct buried SWA cables have been run in professionally, how often a sheath test fails!! And yes it does then need to come out, repaired and reinstalled!!
 
And you’re not the most popular person in the world when you tell the cable lads its got to come out.

We would get cable contractors if there were many runs. For the odd runs our quarry production lads were great, they’d done the job many times and really did know what they were doing. Believe me, get them together en-mass and it’s a frightening sight.

They were quite happy with a pull as on Wednesday afternoon as the quarry and crusher shut down for maintenance so the ideal time. A pull was overtime for them plus it was “job and knock”. They got the full afternoon’s overtime and knocked off once the job was done. I dare anyone to tell them the cables got to come out again, your life wouldn’t be worth living.
 
Was questioning to lead the posts the correct way, I don't deal or have experience with HV so would be out of the conversation but if he's talking about running a 6mm 3core to his shed under his back garden then its all usually manual backfill and wouldn't warrant a sheath test as most domestic sparks don't have the appropriate tester to do so, no column on their test sheets for it either... wasn't questioning the testing of the sheath but the circumstances of the install if he's doing a sheath test as this tends to be past your domestic set ups thus curiosity got me, not often a test mentioned on here.

I bet you can drop this conversation into the forum and 90% of the guys who have buried cable on here will not have done a sheath test, I've not done it often myself but thats more to do with the fact I don't bury many cables. I questioned him because of his strange question at the beginning of using a blue pipe as a sheath - its one of them things that ring alarm bells, so had to clarify exactly what kind of install he's doing, he seems to do a test that most on this forum will never have even done yet asks a weird question to boot when standard ducting would be the way to go, even if he had a 10mm clearance he would not get that swa though that pipe as both would have natural bending in them from storage and the friction would be high over 15m length.

@OP - I wouldn't be going anything less than a 50mm duct to drag a 6mm swa through, it will also allow for future issues to be easily rectified if needed to change the cable.

What is the special test equipment? Would you not just use an insulation resistance meter?
 
What is the special test equipment? Would you not just use an insulation resistance meter?

Its the reason I was asking as to what the voltage was and what kind of work he was actually doing, not all sheath teats can be done with a bog standard Insulation test as this is just a 'pulse method', some companies have requirements that mean a 'Time-Resistance method' is the test needed and most of our combi-testers don't have this option and are not designed to say maintain an Insulation test of 500v/1000v DC for 1minute.

The OP gave no indication as to the nature of the work or who he was contracted under and this may well have sent the thread in a totally different direction. I use Time-Resistance method occasionally myself for motor testing during maintenance checks as it has many advantages against the spot reading method and overcomes a few issues that effects your readings.
 
Last edited:
And you’re not the most popular person in the world when you tell the cable lads its got to come out.

We would get cable contractors if there were many runs. For the odd runs our quarry production lads were great, they’d done the job many times and really did know what they were doing. Believe me, get them together en-mass and it’s a frightening sight.

They were quite happy with a pull as on Wednesday afternoon as the quarry and crusher shut down for maintenance so the ideal time. A pull was overtime for them plus it was “job and knock”. They got the full afternoon’s overtime and knocked off once the job was done. I dare anyone to tell them the cables got to come out again, your life wouldn’t be worth living.

I've become quite used to being the bearer of bad news, ...at the end of the day it's their work and therefore their problem, not mine!!

We undertake sheath tests after the wet sand fill and allowed to compact around the cable, so not quite as bad as testing after complete backfilling has taken place... lol!!
 
What is the special test equipment? Would you not just use an insulation resistance meter?

I used a bog standard Megger @500V.
You’re not testing insulation as such. You’re ensuring the integrity of the outer serving. We used quarry sand straight out of the washing plant, sopping wet and it soon consolidates around the cable. The damp will soon find its way in to any damage.

The insulation tests Damien mentioned would usually be of five minutes duration, sometimes more for long runs as they take time to charge. Our Megger could read to 100TΩ, 100,000,000,000,000Ω.
It gave one or two some nasty bites. The best one was getting the engineering manager, his own fault for crossing the test area barriers. I’m sat in the substation watching the reading gradually rising when it suddenly shot down and I heard a squeal. Served the silly bugger right.
Others got caught trying to take the leads off before the Megger had discharged the cable.
 
I was a little surprised the first time i ever mentioned the ''Sheath Test'' on the forum, very few had ever heard of the term let alone know how to perform or indeed ever conducted a sheath test. We've since had people here trying to conduct a sheath test with the SWA connected to switch boards etc, and those asking what IR value is acceptable for a SWA sheath test!!
 

Reply to Tight fit or room to spare? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
Has anyone had this experience or could offer advice please? I have a 9.5Kw shower, it is fed from the DB in 10mm T&E, a run of approximately...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock