L

LeighSawczyn

Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
 
SWA shouldn't get moisture ingress unless you have damaged it during installation, why go to the trouble of putting it in pipe?
 
Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
Measure the diameter of the cable. If it's less than the alkathene then it will fit. If it isn't it won't
 
If it's there for the long haul then why not add a barrier, anything that slows down corrosion is a good thing as far as I'm concerned, what if it got a scratch in the sheath whilst laying it and the armour corroded? I don't fancy going back to it for free.
 
If it's there for the long haul then why not add a barrier, anything that slows down corrosion is a good thing as far as I'm concerned, what if it got a scratch in the sheath whilst laying it and the armour corroded? I don't fancy going back to it for free.

I agree that it's prob best to put it in a duct, due to sharps/stone in the backfill material but put it in a proper cable duct as Ruston says you wouldn't want people thinking it's a water pipe. Plus if you put it in a a proper cable duct it would be easier to replace should some one have to at any point in the future, you would have a hell of job trying to replace a SWA through a bit of 25mm poly pipe lol
 
Sheath test???? What voltage and nature of the installation are we discussing here!


Not sure where or how you were trained but swa is good for direct burial and if not exposed to corrosive chemicals or mechanical hazards then will be good for many decades, there is really something wrong with your installation methods if you manage to damage the outer sheath to the extent it lets moisture through to the armour, unless your using mechanical means to back fill and compact the ground.
Is there an inherent risk of damage during or after its been buried?

Having said this ducting is commonly used where the costs of servicing, replacing the cables would be high in the event of a failure, in this case use the correct cable duct, depth, burying methods and hazard marker tape or is this for a little garden number - supply to a shed/garage.
 
Last edited:
Good point leesparkykent & ruston. Could leave a plumber in a spot of bother if he tried to tee off for a water supply haha. Mind you the yellow warning tape above should be a clue.
Generally...Black ducting is used for electric cables. U/G cables are black including DNO's mains cable. However years ago and still in use is the old plastic water pipes which are also black. So take nothing for granted. Do the job right first time
 
Sheath test???? What voltage and nature of the installation are we discussing here!

What difference does the voltage make? A sheath test should be done on any UG cable to confirm the integrity of the serving. The only exception I would make is for tarred hessian serving as it is designed to allow leakage of circulating currents.
 
Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
The 25mm dimension of polyethylene pipe usually refers to the outside diameter so internal it will be a ball-hair over 20mm. I assume you're using a 2-core in which case it'll be around 17mm dia so it's going to be a tight squeeze and probably won't be an easy pull for 15 meters but it should be possible if you pull the cable through the pipe first with a fishtape then put it in the ground afterwards. I'd personally go with a larger duct like a 40mm because I hate struggling with stuff like that and I'd plan the job for a warm day when it'll be easier to get everything rolled out nice and straight.
 
What difference does the voltage make? A sheath test should be done on any UG cable to confirm the integrity of the serving. The only exception I would make is for tarred hessian serving as it is designed to allow leakage of circulating currents.

Was questioning to lead the posts the correct way, I don't deal or have experience with HV so would be out of the conversation but if he's talking about running a 6mm 3core to his shed under his back garden then its all usually manual backfill and wouldn't warrant a sheath test as most domestic sparks don't have the appropriate tester to do so, no column on their test sheets for it either... wasn't questioning the testing of the sheath but the circumstances of the install if he's doing a sheath test as this tends to be past your domestic set ups thus curiosity got me, not often a test mentioned on here.

I bet you can drop this conversation into the forum and 90% of the guys who have buried cable on here will not have done a sheath test, I've not done it often myself but thats more to do with the fact I don't bury many cables. I questioned him because of his strange question at the beginning of using a blue pipe as a sheath - its one of them things that ring alarm bells, so had to clarify exactly what kind of install he's doing, he seems to do a test that most on this forum will never have even done yet asks a weird question to boot when standard ducting would be the way to go, even if he had a 10mm clearance he would not get that swa though that pipe as both would have natural bending in them from storage and the friction would be high over 15m length.

@OP - I wouldn't be going anything less than a 50mm duct to drag a 6mm swa through, it will also allow for future issues to be easily rectified if needed to change the cable.
 
Last edited:
Think E54 will confirm this, it’s standard practice to confirm the integrity of the outer serving a few days after the back fill has been done no matter what the system voltage is.

Most of our UG supplies relied on the armour as the earth (no CPC then) to have it corrode away could be disastrous. In reality it never would be that bad as the numerous X linked cables maintained integrity.
We used high conductivity armouring where 1 in 5 armours is tinned copper. These cables are special order, you put one at risk by poor installation methods and there would be all hell to pay.

A sheath test would be normal before the ends were connected. I don’t know what voltage E54 uses but I’ve always used 250V DC between the armours and earth.
 
We don't always sheath test SWA's but if we do we usually common together all the conductors and the sheath and run 1kV through it which is usually what their ins is rated to.
 
I agree that it's prob best to put it in a duct, due to sharps/stone in the backfill material but put it in a proper cable duct as Ruston says you wouldn't want people thinking it's a water pipe. Plus if you put it in a a proper cable duct it would be easier to replace should some one have to at any point in the future, you would have a hell of job trying to replace a SWA through a bit of 25mm poly pipe lol


If it has been installed correctly before you backfill the excavation the cable should be covered with a layer of sand to stop the cable being damaged by stones or sharps.
 

Reply to Tight fit or room to spare? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top