- Reaction score
- 5,633
Afternoon all..
I have just completed an EICR and came across the following :
1. Is the black tarry substance Pitch?
The homeowner is unsure how long it has been there, however it is not completely solid and is slightly sticky to touch indicating that it is still getting too hot at times and leaking? I will be contacting DNO but wanted to get some more information from those who are experienced with this?
Max demand is approx 50A so I would be more concerned with loose connections in the DNO's equipment.
2. TN-S is supplied by a BS951 clamp which I understand was done for a period. My concern is that the 6mm bare cable from the clamp to the MET is just connected to the sleeve of the clamp that is moveable. It is a firm connection to that part of the clamp via the bolt, but just looks awful. I'll tell the DNO about this as well but again wanted some opinions please?
Ze = 0.17Ω
Cut out fuse 100A (not actually seen - but stated on cut out)
Thanks.
I have just completed an EICR and came across the following :
1. Is the black tarry substance Pitch?
The homeowner is unsure how long it has been there, however it is not completely solid and is slightly sticky to touch indicating that it is still getting too hot at times and leaking? I will be contacting DNO but wanted to get some more information from those who are experienced with this?
Max demand is approx 50A so I would be more concerned with loose connections in the DNO's equipment.
2. TN-S is supplied by a BS951 clamp which I understand was done for a period. My concern is that the 6mm bare cable from the clamp to the MET is just connected to the sleeve of the clamp that is moveable. It is a firm connection to that part of the clamp via the bolt, but just looks awful. I'll tell the DNO about this as well but again wanted some opinions please?
Ze = 0.17Ω
Cut out fuse 100A (not actually seen - but stated on cut out)
Thanks.