HappyHippyDad

-
Esteemed
Arms
Reaction score
5,629
Afternoon all..

I have just completed an EICR and came across the following :

black tar on supply cable.jpgBS951 clamp on TN-S.jpg

1. Is the black tarry substance Pitch?
The homeowner is unsure how long it has been there, however it is not completely solid and is slightly sticky to touch indicating that it is still getting too hot at times and leaking? I will be contacting DNO but wanted to get some more information from those who are experienced with this?

Max demand is approx 50A so I would be more concerned with loose connections in the DNO's equipment.

2. TN-S is supplied by a BS951 clamp which I understand was done for a period. My concern is that the 6mm bare cable from the clamp to the MET is just connected to the sleeve of the clamp that is moveable. It is a firm connection to that part of the clamp via the bolt, but just looks awful. I'll tell the DNO about this as well but again wanted some opinions please?

Ze = 0.17Ω
Cut out fuse 100A (not actually seen - but stated on cut out)

Thanks.
 
Wow.. Southern Electric move fast!

Just got off the phone to them and they are going straight around..
 
Just contacted Southern electric for an update.. actually on the phone at the mo!

They say nothing wrong?

Is leaking Pitch ok?

Is that connection to the clamp ok?
 
No.
It would normally suggest overheating within the Cutout joint
Are there any Children in the household, or any that visit..

Well they have said because it is not dripping or hot that it is not an emergency which I guess makes sense. My concern is that they are planning on leaving it like that without doing anything else. Unfortunately my inexperience lets me down here and I dont know if I'm making a mountain out of a mole hill!

I have been given another number to ring on monday and they state they may then send someone out to do some work if needed, but they have basically said all is fine and will only make another visit if I ring and ask.

Also, I cant believe that clamp connection is ok. I can understand that BS951 clamps were used for a while, but that is not my worry. It is the way it is connected to the clamp. Again.. not an emergency as Ze=0.14, but it's hardly a very stable looking connection to the flapping sleeve of the clamp is it??

As for children.... Yes.... 2, one aged 6 and another aged 10!
 
Last edited:
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.
 
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.

Thanks Dave,

It does look slightly different to a 951. It is more they way it is connected. Can you see from the picture what I am getting at? The fact that it is connected to the flapping sleeve rather than firmly against the clamp as you would see with a 951?

BS951%20clamp%20on%20TN-S.jpg
 
If there's no overheating detectable it will probably last years or even decades as it is so I wouldn't lose sleep over it. I'd still call them or get the customer to call them on Monday and insist they make the repairs and upgrade the earth connection.
 
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.

Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!
 
If there's no overheating detectable it will probably last years or even decades as it is so I wouldn't lose sleep over it. I'd still call them or get the customer to call them on Monday and insist they make the repairs and upgrade the earth connection.

Thanks for that Marvo.

I will call them on monday and push it a little I think. I think it would be wrong to just think 'oh well, I've called the DNO it's their responsibilty now'.
 
Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!
But what is the copper equivalent csa of a 10mm x 0.5mm strip of flexible steel?
 
Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!

You might be right, I've got the old regulations at home so I can look up what the required size was at the time, it may be 7/044.
 
Thanks Dave,

It does look slightly different to a 951. It is more they way it is connected. Can you see from the picture what I am getting at? The fact that it is connected to the flapping sleeve rather than firmly against the clamp as you would see with a 951?

I am familiar with that type of clamp yes, it's quite common in the SSE area. There is another one which is just that length of that band wrapped round the lead sheath with a bolt and two wedge shaped nuts to hold it tight, then a nut and bolt with a castle washer through the band in exactly the same way.
Is there a castle washer on that termination?
 
But what is the copper equivalent csa of a 10mm x 0.5mm strip of flexible steel?

Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!
 
Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!

... well, a clamp is a ring ... therefore ... still way too small!
 
Last edited:
I am familiar with that type of clamp yes, it's quite common in the SSE area. There is another one which is just that length of that band wrapped round the lead sheath with a bolt and two wedge shaped nuts to hold it tight, then a nut and bolt with a castle washer through the band in exactly the same way.
Is there a castle washer on that termination?

I'm sorry Dave, I dont know.
 
... well, a clamp is a ring ... therefore ... still way too small!

Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.
 
Last edited:
Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!
k1/k2 * S
k1 for copper is 143, k2 for steel is 51, S= 3.63mm²
so S for steel needs to be (143/51)*3.63 = 10mm², you only have 5mm² (approx)

Hope they actually do something about it.
 
Thanks Richard..

Of course!! I'd only just been looking at table 54.2!

I've never used the K factor for steel before.. and there was me trying to be all clever with conductivity ratios.. just looking foolish really! :smile5:
 
Last edited:
Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.

There shouldn't be a cpc connected to the clamp at all!
 
I had a loose TN-S clamp on a CU change the other day - so I got the DNO out and they said it was fine,
different rules for them and us I suppose!
 

Reply to TN-S with a BS951 clamp and black tar covering supply cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just completed an EICR. The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this...
Replies
7
Views
3K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
I have just carried out an EICR at an old property and found this issue with the main earthing conductor. It has a TN-S system but the earthing...
Replies
32
Views
5K
Hi all. I'm currently training as an electrician so would like your views on this for clarity and if I need to get someone in? I have just moved...
Replies
9
Views
2K
Hi, Can I ask some advice on what to bury please? This is the the front of my house in plan view. House at the bottom. Porch at the bottom left...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock