Discuss TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

A

AdamGiguere

Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

IMG_3970.PNG
 
Hi Westward10

No they have not done anything...

L-N still reads 0.44 (but as all circuits are protected by rcd's isn't so bad)

But L-E is far too high.....
 
They haven't mentioned about the L-E reading which is why I'm a little concerned as I'm aware the highest should be recorded....

But in any case the L-N and L-E readings should be more or less the same for TNCS...

I'm just wondering what could be the cause of the high ZE on L-N...

The only thing I can think of is the earthing connection could be damaged somewhere.

Perhaps an earth rod would fix.
 
They have mentioned this yes, however any board I test L-E at I get Ze of about 9 ohms, the same as when I test Ze at end of circuits I get 9 ohms.

I will call them tomorrow but I'm sure they'd have checked both L-N & L-E surely.

If so why am I getting 9 ohms...baffling me...
 
They have mentioned this yes, however any board I test L-E at I get Ze of about 9 ohms, the same as when I test Ze at end of circuits I get 9 ohms.

I will call them tomorrow but I'm sure they'd have checked both L-N & L-E surely.

If so why am I getting 9 ohms...baffling me...
well it's the pen conductor getting tested so if your testing at the consumer unit L-E it would be the same result more or less as testing L-N unless the earth connection going into the cut out needs attention giving you a high impedance
 
I have had this on PME where there is no connection to the supply neutral. So to clarify you have 0.44 L/N and 9.00 P/E?
 
Reading the OP note from DNO, they have provided PME at 0.44 Ohms. They expect the Electrician to connect to the new PME tail and confirm you now have Ze of 0.44 and that it is sufficient to meet ADS in the installation.
Have you done that?

Stuggling with their wording and action to be taken. When they say

When they say provide new PME tails what do they mean exactly...?
 
well it's the pen conductor getting tested so if your testing at the consumer unit L-E it would be the same result more or less as testing L-N unless the earth connection going into the cut out needs attention giving you a high impedance

When you say the "cut out" what do you mean?

Understand the N and E are one in the same more or less but need to sign off the work but at each point measuring Ze (L&E) it's far to high -
 
The cut out does not come with the earth brass bar as shown above the 25mm earth comes from elsewhere - I'll have to investigate further.

As there must be a problem with the earthing connection?

Just baffling as to why the DNO have not picked this up, would they have just done the test between L-N?

Surely not?
 
Not of the origin - I should have. Apologies...

I'll question the DNO tomorrow when I call.

I'll have to return to the site. There must as you mentioned be something wrong with the earth connection but I couldn't for the life of me see anything wrong earlier when I was looking....
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, I've had an unusual result from taking a Ze at a clients house and wondered what everyones take on it would be: The property is TN-C-S A Ze...
Replies
9
Views
4K
R
Called out to a problem in a remote rural property, TNCS 100a single phase supply, overhead lines. Testing after sorting the issue my MFT flashed...
Replies
6
Views
2K
radiohead
R
Doing an EICR earlier and got some wierd readings not experienced before, thankfully property is empty. I did a Zdb on a TNC-S system and got an...
Replies
4
Views
2K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock