Discuss TNCS Outbuilding earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net

I have exported the equipotential zone to outbuildings before with no problems and mostly without having to bond any extraneous parts, because there have been none. Nice low ZS readings. No problem. (unless "Rodman" sees this! He thinks it is a big no no for some reason)
 
I have exported the equipotential zone to outbuildings before with no problems and mostly without having to bond any extraneous parts, because there have been none. Nice low ZS readings. No problem. (unless "Rodman" sees this! He thinks it is a big no no for some reason)


read post#2
 
I have read all the posts! What about the house TNCS then? The world is all if's and but's!


run a 2 core SWA to the hut, an RCd cu in the hut with TT supply from the SWA, and an earth rod at the hut end. SWA earthed at the supply end but the SWA earth insulated at the load end.
 
Where do all these rumours come from.........?
Its all written in black and white (with green covers) :p
Exporting TNCS or PME is fine!! along as any extraneous conductive part is connected to the MET.
How many times have i heard the you can't do this rumours only to look in the regs to prove them wrong ;) haha
 
I have seen this on here many times. There seems to be an obsession about exporting the equipotential zone in outbuildings. Nothing wrong with it and its fine according to the Regs. Period.
 
I can see there point about loosing the neutral.... as I've seen it a few times!!
But if it was that much of a concern TNCS supplies would be banned ;) and it shouldn't occur with PME
 
I have seen this on here many times. There seems to be an obsession about exporting the equipotential zone in outbuildings. Nothing wrong with it and its fine according to the Regs. Period.


In that case you need to ensure that you Zdb at the hut complies with the max for the earthing system that you are exporting.

are you going to calculate the distribution cable R1+R2, and hence calculate the Zdb, as well as the cable size for the expected load? not many do.

or as most people, just design for the expected load and then install the cable, and then take the Zdb measurement afterwards? and hope that it is within the regs?
 
Last edited by a moderator:

Reply to TNCS Outbuilding earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock