Discuss tray bonding in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
2
what do most do with tray to ensure its bonded, earth tags at each joint like on galv trunking or are the joins substantial enough, only ask as a dont generally use it but its specced on a job to install for data cabling and can i run power cables in the same tray if i keep them segregated?
 
on tray you need to use earth braids at each joint.Dont use earth tags.I cant see why you couldnt run power and data on the same tray as long as they are segregated but i would check the spec to see if there is anything against it
 
generally use wire basket for data lot easier to install, bond at one end if correct joints are used

- - - Updated - - -

generally use wire basket for data lot easier to install, bond at one end if correct joints are used
 
bit more info , if your using the basket as part of the earthing system it should be bonded at each end and every 15 mtr of the run
CABLOFIL Couplers
The standard IEC 61537 states that coupler resistance must not exceed 50mΩ. The test involves running an electric current trough the system (cable trays + couplers and measuring coupler resistance.
 
Is it cable tray or trunking you intend to use?
These are the earth links for some cable tray or trunking Earth Link | Unitrunk
 
We always earth our cable trays, which are pretty extensive too. We use two copper earth connections at each joint diagonally opposed. Generally our tray/basket work runs are dedicated to either comm's, LV, MV, but if the need arises i have no problem if space allows, to run LV and Comms on the same tray for shorter distances. All our comms cabling is screened and rated 600V anyway...
 

Reply to tray bonding in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
1K
Hi all Regarding bonding of cable tray and basket. Is basket required to be bonded if only data cables installed on it ? plus bonding cable tray...
Replies
28
Views
8K
Hi all Just a question on segregating of cables and other services. I have a tray route to install for a small cafe and going to be supplying...
Replies
0
Views
992
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
844
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock