Discuss tripping induction hob in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
5
Hi guys

Interested in your thoughts here. I recently installed a new circuit to supply an induction hob and oven. The circuit is supplied via a 40 amp rcbo. The rcbo however is intermittently tripping, sometimes when it's not even in use and stone cold I.e no fan etc running. I know the loading is correct and this is not an overload fault.

I'm thinking it's a faulty oven unit/hob unit - it's brand new and straight out the box.

Or do induction hobs require a type c breaker to cope with the inductive load - if that's how they work? Iv fitted induction hobs before in type b breakers and never had a problem.

Any thoughts?

Thanks.
Dan
 
It is quite common for elements to absorb moisture and trip RCD's. This is why it will do it when not in use.
Is the double pole switch off when it is tripping?
 
It may well be a mineral element then. Sometimes drying them out solves the problem, but there is no guarantee that it will not do it again. RCD's are not ideal for cookers unfortunately. (you will have to be ingenious to dry it out lol :wink5::wink5:)
Try the suggestions for IR first though.
 
The very first induction hob I did many moons ago had the same problem, after speaking to the manufacture I was advised to run feed in swa and omit rcd protection as induction hobs had a tendency to trip rcd.

Complete bo***cks I thought but as the cu was literally in the next cupboard and house was still being refurbished this is what I did.

I've never had issues with induction hobs and rcd's since that one but it could be same make? Cant remember make of that one but probably called something like Bonko bought for peanuts off ebay.
 
If the circuit is all ok and test confirm circuit is not faulty you could try the circuit for a short time on an MCB , then once elements have warmed up replace MCB with the RCBo again , worth a try that is of course if the RCBo is not faulty and tests out alright , disconnect circuit completely to carry out the RCD test though..
 
Looks like some electricians on this thread have no concept of what an induction hob is!. It is basically a high power low frequency radio transmitter connected to a coil under each pan location. The pan is heated by eddy currents induced in the pan. Note that such a hob will have a large number of RF filters including caps L to E and N to E. These caps will cause a large amount of leakage current and also provide a good path for any RF noise from elsewhere to earth. I would suggest first clamp it to find out the level of earth leakage and then fit a good RCD that also has transient suppression.
 
Hi guys

Interested in your thoughts here. I recently installed a new circuit to supply an induction hob and oven. The circuit is supplied via a 40 amp rcbo. The rcbo however is intermittently tripping, sometimes when it's not even in use and stone cold I.e no fan etc running. I know the loading is correct and this is not an overload fault.

I'm thinking it's a faulty oven unit/hob unit - it's brand new and straight out the box.

Or do induction hobs require a type c breaker to cope with the inductive load
- if that's how they work? Iv fitted induction hobs before in type b breakers and never had a problem.

Any thoughts?

Thanks.
Dan
Gasp !!!
 

Reply to tripping induction hob in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
946
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock