Discuss Trunking cable capacity in the UK Electrical Forum area at ElectriciansForums.net

D

Ducksy

Hey folks, im wiring in a shower circuit, i've decided on singles in PVC trunking (10mm line/neutral) (4mm CPC) I've worked out my cable factor in trunking as 87.2...................Problem is OSG shows smallest size trunking as 50mm X 38mm Thats way to big!!!!

Can anyone point me in the right direction for the trunking factors for smaller pvc trunking......?

Sorry if it sounds a dumb question but i normally use twin and earth clipped direct......sod fitting that in trunking.

Thanks.
 
If it was singles I would run a 6mm2 haha, I would like to run a 10mm2, but it would be a complete nightmare to connect into the pull cord switch, so 6mm2 would just have to do, but everyone to their own, in a T&E I am aware it is only 4mm2, another silly decision by the cable manufacturers.
 
If it was singles I would run a 6mm2 haha, I would like to run a 10mm2, but it would be a complete nightmare to connect into the pull cord switch, so 6mm2 would just have to do, but everyone to their own, in a T&E I am aware it is only 4mm2, another silly decision by the cable manufacturers.

I would love to use 6mm but the shower is a 10.5kw....in trunking 6mm CCC is only 38a far below the 44a needed :(
 
In over 25 years in the game i have seen numerous bits of trunking either plastic or metal absolutely rammed solid with cables.Plenty of times i have seen whole bottles of fairy liquid and planks of wood and hammers used to crush even more in,and bits of lid tied on with tie wraps because the buckles wont turn.And that is on new build prestige jobs not just lash ups.What is in the OSG quite often bears no resemblance to what happens on site
 
In over 25 years in the game i have seen numerous bits of trunking either plastic or metal absolutely rammed solid with cables.Plenty of times i have seen whole bottles of fairy liquid and planks of wood and hammers used to crush even more in,and bits of lid tied on with tie wraps because the buckles wont turn.And that is on new build prestige jobs not just lash ups.What is in the OSG quite often bears no resemblance to what happens on site

I don't think that could be called a ''Prestige Job'', if that's what's being allowed to happen!!
 
For prestige read lowest possible tender price to the contractor and maximum profit to the developer. I agree with Essexboy7, it happens all the time. I spent a week last month, in an International Banks flagship office sorting out some prestige work that looked just like that!
 
Jubilee line extension
kings cross Eurostar
westfield shopping centre white city
The shard
The Gherkin


To name but a few.And you dont get more prestige then those jobs


Its all down to greed and poor design.At the first sign of trouble the easiest thing to do is admit the containment is too small and rip it out and put bigger stuff in,but that means either the designer admitting they got it wrong or the subby swallowing the cost of labour to rip it out and replace it and neither of hose 2 things are ever going to happen

I suppose you dont have to worry about a fire as theres no room for any oxygen in there!!!!!!!
 
Last edited by a moderator:
Jubilee line extension
kings cross Eurostar
westfield shopping centre white city
The shard
The Gherkin


To name but a few.And you dont get more prestige then those jobs


Its all down to greed and poor design.At the first sign of trouble the easiest thing to do is admit the containment is too small and rip it out and put bigger stuff in,but that means either the designer admitting they got it wrong or the subby swallowing the cost of labour to rip it out and replace it and neither of hose 2 things are ever going to happen

I suppose you dont have to worry about a fire as theres no room for any oxygen in there!!!!!!!


No bloody supervision on site more like, and an electrical contractor that isn't worth a ----!! Never been on a project yet, where it's not part of the electrical contactors responsibility to conform to the standards the specification is based on!! If the stipulated sizes of trunking or any other containment system is not adequate for the job, then it is down to the contractor to raise the issue!! A contractor working on these types of projects will, without doubt have a Quantity Surveyor as part of the team, who would be looking for just this sort of thing, to make ''Extras'' on, for both materials and man-hours!! It's where contractors can make serious money, and why the QS are worth their weight in gold on big projects!! So your explanation makes no sense at all contractually!!
 
Last edited by a moderator:
Agreed mate, I'm totally bewildered by this thread! How long is the bloody run to need a 4mm CPC?!

How does running in conduit change CPC size anyway?

Sorry DN21 i worked the adiabatic out like this

I²=1400²

t = 0.01

k= 115.....so

S= √(1400²×0.1)/115=3.8mm²

i think you read it wrong no one said running in conduit would change CPC's CSA
 
Sorry DN21 i worked the adiabatic out like this

I²=1400²

t = 0.01

k= 115.....so

S= √(1400²×0.1)/115=3.8mm²

i think you read it wrong no one said running in conduit would change CPC's CSA

S= √(1400²×0.01)/115=1.22mm²

Double check the 0.01 value with the manufacturer but I'm 99.99% sure you'd be fine with a 1.5mm CPC :)
 
If it was singles I would run a 6mm2 haha, I would like to run a 10mm2, but it would be a complete nightmare to connect into the pull cord switch, so 6mm2 would just have to do, but everyone to their own, in a T&E I am aware it is only 4mm2, another silly decision by the cable manufacturers.

Wtf is this lol??
so you'd like to use a 10mm cpc for a 10mm shower circuit given the choice ? why ?
a silly decision by the cable makers to use 4mm ?? how ?

theres a whole heap of wrong in that post.
;-)
 
If running singles in a non metal cable containment system Biff we industrial sparks tend to use the same sized CPCs as phase conductors, 2.5 phase with 2.5 cpc, 6mm2 phase with 6mms cpc etc, hence my comment about a 10mm2 which did have a bit of jest in the post, as for the 4mm2 in a 10mm2 Twin and Cpc, I have always concidered a 4mm2 small in comparison, I would much prefer a 6mm2 cable, I don't like the CPC less than half the size of the phase conductors, unless metal containment is used, it's all wrong IMO, and to add to it, I would like to see the CPC actually sleaved in twin and CPC cables too, it is just lazy and money pinching to have the CPC bare, Now be a good boy and pick the daylights out of that comment
 
If running singles in a non metal cable containment system Biff we industrial sparks tend to use the same sized CPCs as phase conductors

By 'We' you are including myself in this category and I don't and never will unless calculation warrants a CPC the same size or larger than the live conductors. If I caught any of my lads running a 10mm CPC with 10mm live conductors I would be asking questions! When designing we only use cable that is neccessary, every ounce of wasted and unneccessary copper is paid for out of my pocket at the end of the day! :)
 
Just trying to get Biff to bite, you have probably ruined it now, and I thought we were in for a Friday night boxing match, ah well were done now, I give in he was right, I will have to start something else going now.
 
If running singles in a non metal cable containment system Biff we industrial sparks tend to use the same sized CPCs as phase conductors, 2.5 phase with 2.5 cpc, 6mm2 phase with 6mms cpc etc, hence my comment about a 10mm2 which did have a bit of jest in the post, as for the 4mm2 in a 10mm2 Twin and Cpc, I have always concidered a 4mm2 small in comparison, I would much prefer a 6mm2 cable, I don't like the CPC less than half the size of the phase conductors, unless metal containment is used, it's all wrong IMO, and to add to it, I would like to see the CPC actually sleaved in twin and CPC cables too, it is just lazy and money pinching to have the CPC bare, Now be a good boy and pick the daylights out of that comment

not much of a challenge old bean , as everthing you just said is at complete odds with using the adiabatic to properly size a cpc with regards to evaluating thermal constraints.
and whats with all this "we industrial sparks" bullcrap ? you must think you're the only non domestic spark or something else grand and deluded.
 
Just trying to get Biff to bite, you have probably ruined it now, and I thought we were in for a Friday night boxing match, ah well were done now, I give in he was right, I will have to start something else going now.

beer + popcorn ready
ding ding round 1.
 
to add to my first post though, although I was Jesting about the 10mm2, I was serious about the 6mm2, I really don't like CPCs less than half the size of the phase conductors, and do believe Twin and Earth cables should have the earths sleaved not bare, okay lets go round one, put them up :dita:
 

Reply to Trunking cable capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
863
Ok all, I'm looking at a shower install and need a bit of advice selecting the correct cable for the job. The customer has a 10.5 KW shower...
Replies
7
Views
1K
I'm slowly attempting to upgrade and rewire the house I'm in. Started by doing the consumer unit. Got the dno replacing my cable coming as its way...
Replies
12
Views
4K
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Replies
3
Views
2K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock