- Reaction score
- 25,489
There is no requirement for a protective device on a TT system to be double pole just that it disconnects in the event of a fault.
Discuss TT system, RCD or RCBO in the UK Electrical Forum area at ElectriciansForums.net
My interpretation is that part of the installation is on an RCD and part isn't, it's possible that a N-E fault on a single pole RCBO circuit could result in the other RCD operating for that fault because a parallel path would remain in place even if the RCBO tripped. A DP RCBO would prevent that. I do not think it is a requirement, but if possible I would fit a DP device if I was altering the circuit protection as part of the work carried out.
Reply to TT system, RCD or RCBO in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.