Discuss TT With Amd 3 boards in the UK Electrical Forum area at ElectriciansForums.net

soulman

-
Arms
Reaction score
94
Hi, when installing a consumer unit in domestic premises, I have been swopping out the main switch for an S type 100ma rcd. The reason I have been doing this is advice given in the on-site guide. PG 34 & 35. Dual RCD boards : Stating that there is insufficient fault protection of the single insulated conductors from the bottom of the main switch to the top of the rcd's.
I have come across a few installs recently (TT) that don't have a rcd main switch, I queried this with the Technical Helpline & they state I don't need one.
Does anyone else install a RCD main switch.

Cheers
 
Hi, when installing a consumer unit in domestic premises, I have been swopping out the main switch for an S type 100ma rcd. The reason I have been doing this is advice given in the on-site guide. PG 34 & 35. Dual RCD boards : Stating that there is insufficient fault protection of the single insulated conductors from the bottom of the main switch to the top of the rcd's.
I have come across a few installs recently (TT) that don't have a rcd main switch, I queried this with the Technical Helpline & they state I don't need one.
Does anyone else install a RCD main switch.

Cheers

It's not the advice I received from Elecsa Technical. A3 Dual CU's with a TT supply will require S Type for the reason you've given, either as a main switch, or as a stand alone.
 
Soulman, how was this advice obtained?

I very rarely now make contact with technical via phone, always by email. I find you get a more considered and in depth response that way, with specific regulations referred to (not specific, in this case). I think via phone, they are sometimes too quick to finish the call, and your question can get 'lost in translation'.
 
Hi, when installing a consumer unit in domestic premises, I have been swopping out the main switch for an S type 100ma rcd. The reason I have been doing this is advice given in the on-site guide. PG 34 & 35. Dual RCD boards : Stating that there is insufficient fault protection of the single insulated conductors from the bottom of the main switch to the top of the rcd's.
I have come across a few installs recently (TT) that don't have a rcd main switch, I queried this with the Technical Helpline & they state I don't need one.
Does anyone else install a RCD main switch.

Cheers
If it's a dual rcd consumer unit the tails should enter the metal enclosure through a insulated stuffing gland to protect against abrasions of the tails.
I would install an s type 100mA rcd as the main switch to protect the tail links inside the consumer unit which if become loose and short out on to the casing and becomes a dangerous situation. technically the tails and links will need a 1 second disconnection time so the s type will give you this.
 
The Elecsa and NICEIC help desk is awful and not to be trusted. .....

Have to disagree with you there Murdoch. Where I've had some instances where they have sat on the fence, for the most part I've received correct, good & useful advice. Ringing them, as I I've said, doesn't get the best result.
 
Hi, Thanks for replies,
Yes it was via telephone. They said that as a long as a stuffing gland is used for the tails (Which would always be used) the manufacturers have designed unit for all situations. I explained in detail that I have given a code 2 observation for this during a periodic. My personal take on it is, the on site guide recommends the use of an rcd to protect the conductors from the main switch to the rcd's as they only have insulation & no sheath. Therefore in my opinion it is unlikely to happen, but still has the potential to happen & cause a dangerous situation, therefore I will continue to use a RCD as the main switch. I did ask Elecsa when AMD 3 boards come into play, if I could use a REC2 Enclosure before the board with a 100ma S type. They said no as the REC2 enclosures are plastic. Which to me is crazy as this would also protect the tails entering the board.
 
Hi, Thanks for replies,
Yes it was via telephone. They said that as a long as a stuffing gland is used for the tails (Which would always be used) the manufacturers have designed unit for all situations. I explained in detail that I have given a code 2 observation for this during a periodic. My personal take on it is, the on site guide recommends the use of an rcd to protect the conductors from the main switch to the rcd's as they only have insulation & no sheath. Therefore in my opinion it is unlikely to happen, but still has the potential to happen & cause a dangerous situation, therefore I will continue to use a RCD as the main switch. I did ask Elecsa when AMD 3 boards come into play, if I could use a REC2 Enclosure before the board with a 100ma S type. They said no as the REC2 enclosures are plastic. Which to me is crazy as this would also protect the tails entering the board.
But if you fit plastic enclosure switchgear it defeats the object of a non combustible DB.......The RCD enclosure would now be the 'fire hazard'.
 
For TT the OSG suggests an insulating gland and a 100mA time delay RCD main switch if a dual RCD board is used due to the single insulation on the internal tails to the RCDs. If an all RCBO board is used the time delay RCD can be omitted. For a standard domestic install, single pole RCBOs are fine.
 
For TT the OSG suggests an insulating gland and a 100mA time delay RCD main switch if a dual RCD board is used due to the single insulation on the internal tails to the RCDs. If an all RCBO board is used the time delay RCD can be omitted. For a standard domestic install, single pole RCBOs are fine.
What is a non standard domestic install:D
 

Reply to TT With Amd 3 boards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
880
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
328
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock