Discuss Two Lutron RA2 Switches - both switched on, and RCD trips, either on and no problems in the DIY Electrical Advice area at ElectriciansForums.net

Paul F

DIY
Reaction score
0
Only a DIY'er here, usually safe and competent enough to fix straight forward problems, but this one has me stumped. I have two outside lighting circuits running through Lutron RA2 dimmers. Both go back to a Hager MTN106 RCD. All been working fine for over a year, but now the breaker keeps tripping. All LED lamps and well within 150w capacity of each dimmer controller. Common feed from the RCD split to the two circuits, and I can leave either circuit connected independently without problems. As soon as I connect both circuits, the RCD trips. Changed the Wago connector blocks hooking it all together in the junction box and tried a differnet RCD but the same problem. All installed by a qualified electrician, but assumed it would be an easy fix without calling him back. Any ideas?
 
I'm not clear what the outside circuits comprise, but it is possible there is a small amount of earth leakage in each circuit, where each is not enough to trip an RCD, but together they do. Such leakage can be inherent in the design of acessories or PSU filters, or occur through the ingress of moisture etc.
You could check this out by using an earth leakage clip-on milliammeter on the supply to each circuit.
 
I'm not clear what the outside circuits comprise, but it is possible there is a small amount of earth leakage in each circuit, where each is not enough to trip an RCD, but together they do. Such leakage can be inherent in the design of acessories or PSU filters, or occur through the ingress of moisture etc.
You could check this out by using an earth leakage clip-on milliammeter on the supply to each circuit.
One circuit has 8 bollard lights and the other has 4 bollards and 8 recessed spots in the side of a planting bed. All fittings are IP65 rated but water ingress is a distinct possibility. I hadn't thought about the combined effect of earth leakage. Will investigate further. Many thanks
 

Reply to Two Lutron RA2 Switches - both switched on, and RCD trips, either on and no problems in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Our family room is part of an addition built a few years ago. We had an issue with nuisance tripping on an AFCI and the electrician came and...
Replies
2
Views
1K
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
394
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
287

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock