Discuss two radials on 16 a mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

ac/dc

-
Reaction score
0
Hi All
Today I came across 2 x 2 radials on 16 a mcb's. Both on 2,5 mm .
One is for KTCH and the other for the 2 bed flat .
They were suppose to be rings , but for some reason they are radials .
If you do T & I , what would you put on a test sheet for R1 + R2 and ZS
Thx
 
What is a KTCH?

What do you mean when you say they were supposed to be rings?

You put down the measured values in the appropriate boxes for the circuits you have tested


Sent from my iPad using Tapatalk
 
Hi DS
THx .for your replay .
I was checking the elect. certs . from 10 yers ago and there were 2 rings on that 2 bed flat.
One for kitchen and one for the rest of the flat.
There were on 32 a mcb.
Now there are no 32A mcb , there are 16 a mcb .
After testing them , ther is no connt . on both rings.
They are radials .
there is no space for an extra mcb's .
If you do T & I what would you do .
THx
 
as the cables cannot be overloaded, there is no apparent potential danger, but probably will give rise to nuisance tripping.therefore, i'd code it C3. remedial works are to be discussed with customer. give them the options and let them decide. ( i am assuming the circuits are RCD protected ).
 
Hi DS
THx .for your replay .
I was checking the elect. certs . from 10 yers ago and there were 2 rings on that 2 bed flat.
One for kitchen and one for the rest of the flat.
There were on 32 a mcb.
Now there are no 32A mcb , there are 16 a mcb .
After testing them , ther is no connt . on both rings.
They are radials .
there is no space for an extra mcb's .
If you do T & I what would you do .
THx

Your post is still very confusing, could you please take the time to write in a more coherent manner and proof read your posts, there is no time limit to how long you take to make a post and you will get far more help if you can communicate clearly.

At the moment it sounds like there is nothing wrong and nothing to do, presumably a fault has occurred and the only way this could be solved was to cut out the bad section and make the circuit a radial with two branches. Though it is very odd for similar faults to happen to two different circuits.
 
as the cables cannot be overloaded, there is no apparent potential danger, but probably will give rise to nuisance tripping.therefore, i'd code it C3. remedial works are to be discussed with customer. give them the options and let them decide. ( i am assuming the circuits are RCD protected ).

I would have said no code to be given if this is an EICR, unless talking to the occupier reveals that a serious nuisance tripping problem is occurring
 
Hi DS
THx .for your replay .
I was checking the elect. certs . from 10 yers ago and there were 2 rings on that 2 bed flat.
One for kitchen and one for the rest of the flat.
There were on 32 a mcb.
Now there are no 32A mcb , there are 16 a mcb .
After testing them , ther is no connt . on both rings.
They are radials .

there is no space for an extra mcb's .
If you do T & I what would you do .
THx

You've lost me.

How many MCB's are you referring to?

How many cables are in the MCB's?
 
Hi
I wanted to separate those radial circuits but there is no space for extra mcb .
My only problem is the R1 + R2 and Zs.
Would you consider them as a 2 radials circuits .
Even regs is confusing when it comes to those situations.
thx
 
Hi
I wanted to separate those radial circuits but there is no space for extra mcb .
My only problem is the R1 + R2 and Zs.
Would you consider them as a 2 radials circuits .
Even regs is confusing when it comes to those situations.
thx

No they are not.

Please answer post # 8
 
You've lost me.

How many MCB's are you referring to?

How many cables are in the MCB's?

Hi M
There are 2 mcb , both at 16 A.
in both of them there are 2 wires .
First thought would be there is a ring in there , but there is no contin. on L- L and the rest.
Both are radials.
IMO there is no problem as there are on 16 A mcb .
Would you consider them as one radial circuit or two radials.
Would you write the highest reading for r1 + r2 after you test both cables .
THx
 
Hi M
There are 2 mcb , both at 16 A.
in both of them there are 2 wires .
First thought would be there is a ring in there , but there is no contin. on L- L and the rest.
Both are radials.
IMO there is no problem as there are on 16 A mcb .
Would you consider them as one radial circuit or two radials.
Would you write the highest reading for r1 + r2 after you test both cables .
THx

1x ocpd = 1x circuit regardless of the number of conductors connected.

Why on earth would you assume a circuit connected to a 16A mcb is a ring final circuit when the standard ring is a 32A circuit?
 
As far as I can read this.
Past the old EIC said there was two rings
Now there is two radial on each of.the two mcb guess down rated to 16A from the 32A it problerly was when they where rings

R1+R2 is the far point in the radial which every is the worse case ie the highest
Both radials on both circuits will need to be tested and not the far point for any one else
 
Hi M
There are 2 mcb , both at 16 A.
in both of them there are 2 wires .
First thought would be there is a ring in there , but there is no contin. on L- L and the rest.
Both are radials.
IMO there is no problem as there are on 16 A mcb .
Would you consider them as one radial circuit or two radials.
Would you write the highest reading for r1 + r2 after you test both cables .
THx


r1 and r2 on a radial? as far as I knowr1 and r2 are readings required for a RFC

2 16A cbs both have 2 cables, confused.com
 
Last edited:
Also said on the last report these radials where rings
So on the last report on the system they would of had the r1 r2 rn
As far as I can read these rings have been broken and places on 16A breaker
So what was once two rings have become four radials over two circuits
 
to clarify. each 16A MCB has 1 radial circuit consisting of 2 branches.
 
to clarify. each 16A MCB has 1 radial circuit consisting of 2 branches.

So OP:

Step 1 - locate the sockets / outlets on "both" branches.

Step 2 - I & T each branch

Step 3 - record the higher readings however if, for example 1 leg is short and has low IR and the other is long and has good IR I would be inclined to record both sets of readings on the schedule of inspections..... and add a note in the inspection comments section.
 
So OP:

Step 1 - locate the sockets / outlets on "both" branches.

Step 2 - I & T each branch

Step 3 - record the higher readings however if, for example 1 leg is short and has low IR and the other is long and has good IR I would be inclined to record both sets of readings on the schedule of inspections..... and add a note in the inspection comments section.

At last, a straightforward answer to (an initially befuddled) question.
Truth is, I've come across many electricians who don't know exactly how best to test & record such a scenario, so let's not be too hard on the OP. And yes, electricians mixing up their r1 & R1 etc, gets me too!
 
At last, a straightforward answer to (an initially befuddled) question.
Truth is, I've come across many electricians who don't know exactly how best to test & record such a scenario, so let's not be too hard on the OP. And yes, electricians mixing up their r1 & R1 etc, gets me too!
some guys just don't know their arse (r's ) from their elbows.
 
Trying to get this thread back on topic:- You can not have have 2 circuits from the same OCPD. You can have one radial socket circuit with a spur from the MCB if feeding only one point!

Discuss?
 
Trying to get this thread back on topic:- You can not have have 2 circuits from the same OCPD. You can have one radial socket circuit with a spur from the MCB if feeding only one point!

Discuss?
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.
 
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.

Branching off a radial is fine from a socket. Branching from a MCB?...... I was thinking along the lines of separation of circuits but at the end of the day, if it was a RFC in the first place it would serve the same floor/area so no difference really.
 
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.

But remove the RFC leaving the 2.5mm radial with one double outlet on the 32A MCB and it suddenly becomes dangerous and against the regs, much in the same way that an insulated consumer unit will inevitably catch on fire now it's not to regulations.
 

Reply to two radials on 16 a mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
324
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Replies
6
Views
861
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock