Discuss Type 1 SPD at Mains Intake Advice Please on a TNCS in the UK Electrical Forum area at ElectriciansForums.net

John-

-
Reaction score
48
Hi

Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably high lightning strike area. So suggested they should have one. Did some research and was going to use the Hagar SPA4501 along with the metal IU4 enclosure.

But in order to follow the guidance it has to be fitted as close to the mains intake as possible. And i am a bit concerned about the only protection for a metal enclosure, in the mains cupboard, being the DNOs 100A fuses.

The installation consists of the three fuses in the head then the earth and Nutural coming out in 25mm, into a 4 pole rotary, plastic 100A Isolator. Then the tales come out of the load side of the isolator in single insulated, fine stranded 25mm that leads off in Copex to the Sub Mains Dis boards a few feet away.

Was thinking i could install another set of 25mm tales in the load side of the Isolator, then install the SPD directedly below the isolator. So only protection for it / cables is the DNO fuses.

Seeing as the IU4 is metal, was wondering if to install the metal housing within a separate plastic enclosure to prevent a access to touch without a tool?

The cupboard is not locked. It is a small lean to building with large doors, it only contains the meter and the distribution equipment for the site. So a meter reader, IMHO, could be at risk if the case had short. I realise that any short so close should blow the fuse quickly enough, not like a TT situation. So am I being too cautions?

Hypothetically if this was a TT i guess it would have to be installed after the Main RCD?

Thnaks

JOhn
 
is this a 3ph intake into a 3ph system or 3 x singles? Slightly confused.

Either way, my gut tells me you may be overthinking this.... if the board/s are only 'a few feet away' then fit what's appropriate at that point. If there's no other CPD in between the intake and that first board then the DNO's fuses are doing that job regardless of any other devices you install.
 
So it's INTAKE > 100A ISO > 25mm Tri-rate > First DB?
 
If so.... swap out the 100A ISO for an enclosure for the SPD which has an incoming insolator. Same-ish footprint.
 
@Rockingit not sure what you mean. Why would i remove the Isolator? It serves the purpose of allowing us to work on the Dis boards in the mains room? I should have also mentioned that the Isolator feeds two boards, one for general kit, and the other board via a changeover switch for essential services fed via on site generator. In the event of power fail, they manually switch the three position switch to generator that isolates the mains from the 2nd dis board, and introduces the feed from the generator - then they start the generator.

With respect to the SPD I'm just wondering if i need to install a plastic enclosure with the metal one in. I 'think' i am being too cautions?

John
 
@Rockingit not sure what you mean. Why would i remove the Isolator? It serves the purpose of allowing us to work on the Dis boards in the mains room? I should have also mentioned that the Isolator feeds two boards, one for general kit, and the other board via a changeover switch for essential services fed via on site generator. In the event of power fail, they manually switch the three position switch to generator that isolates the mains from the 2nd dis board, and introduces the feed from the generator - then they start the generator.

With respect to the SPD I'm just wondering if i need to install a plastic enclosure with the metal one in. I 'think' i am being too cautions?

John
You'd still have your isolator. HOWEVER...... with this new information, my guess is that you actually need the SPD downstream of the dual supply?
 
Suppression (Type 1) needs to be close to the mains supply, to protect the site from external influences.
Re reading what you wrote earlier: -

"If so.... swap out the 100A ISO for an enclosure for the SPD which has an incoming insolator. Same-ish footprint."

Do you mean provide an SPD and Isolator, in the same enclosure?
 
I would put the SPD in a metal DIN enclosure. If something goes wrong / big strike they might get very hot (though they have solder links to disconnect in that case).

If you can run the cables (25mm tri-rated?) from isolator to DIN box to board then use the sort with the double connections so they have practically no additional inductance. This is the sort I have used (TN-S style):


They also do one more like the common sore with different N-E protection for TT systems:

They are OK with 125A supply fuses for "V wiring" (Kelvin 4-ware style), not requiring any additional protection.
 
Thanks @pc1966 I already have the antisurge device. Will look at ours next time. I was going to just spur off the isolator, hence the lugs so the isolator would have three sets of cables coming out - two to the loads and one set to the SPD. If there was any doubt about the terminals in the isolator taking the three sets of lugs, i was going to use Henley blocks and use insulated and sheathed tri rated cable - or just tales. I need to go back to site and check the options.
 
OK!

Just to add if you had space for the likes of the Hager JK116EA3 (assuming it has to meet amendment 3, I used the glazed one for industrial site) you could put in a 50A D-curve MCB for the SPD if worried about the DNO fuses (or want a quick means of isolation for IR testing) and you could also put in some linked DIN terminals to allow 4 connections for each of L1-3 & N:
  • power in
  • SPD MCB feed
  • board #1
  • board #2
All with minimum distance and inductance to the SPD.

The likes of these terminals allow 35mm cable to be attached and are rated at 125A, but I have not checked if they clear the DIN box (can do later):
These are the jumper bars to link an adjacent pair of terminals together:
You get them up to 10-way but not from RS, think I got mine from these folks:
 

Reply to Type 1 SPD at Mains Intake Advice Please on a TNCS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi We are looking to get an EV charger installed, and I asked for an SPD to be on the new CU that will be required for that. The electrician has...
Replies
11
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock