Hi
Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably high lightning strike area. So suggested they should have one. Did some research and was going to use the Hagar SPA4501 along with the metal IU4 enclosure.
But in order to follow the guidance it has to be fitted as close to the mains intake as possible. And i am a bit concerned about the only protection for a metal enclosure, in the mains cupboard, being the DNOs 100A fuses.
The installation consists of the three fuses in the head then the earth and Nutural coming out in 25mm, into a 4 pole rotary, plastic 100A Isolator. Then the tales come out of the load side of the isolator in single insulated, fine stranded 25mm that leads off in Copex to the Sub Mains Dis boards a few feet away.
Was thinking i could install another set of 25mm tales in the load side of the Isolator, then install the SPD directedly below the isolator. So only protection for it / cables is the DNO fuses.
Seeing as the IU4 is metal, was wondering if to install the metal housing within a separate plastic enclosure to prevent a access to touch without a tool?
The cupboard is not locked. It is a small lean to building with large doors, it only contains the meter and the distribution equipment for the site. So a meter reader, IMHO, could be at risk if the case had short. I realise that any short so close should blow the fuse quickly enough, not like a TT situation. So am I being too cautions?
Hypothetically if this was a TT i guess it would have to be installed after the Main RCD?
Thnaks
JOhn
Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably high lightning strike area. So suggested they should have one. Did some research and was going to use the Hagar SPA4501 along with the metal IU4 enclosure.
But in order to follow the guidance it has to be fitted as close to the mains intake as possible. And i am a bit concerned about the only protection for a metal enclosure, in the mains cupboard, being the DNOs 100A fuses.
The installation consists of the three fuses in the head then the earth and Nutural coming out in 25mm, into a 4 pole rotary, plastic 100A Isolator. Then the tales come out of the load side of the isolator in single insulated, fine stranded 25mm that leads off in Copex to the Sub Mains Dis boards a few feet away.
Was thinking i could install another set of 25mm tales in the load side of the Isolator, then install the SPD directedly below the isolator. So only protection for it / cables is the DNO fuses.
Seeing as the IU4 is metal, was wondering if to install the metal housing within a separate plastic enclosure to prevent a access to touch without a tool?
The cupboard is not locked. It is a small lean to building with large doors, it only contains the meter and the distribution equipment for the site. So a meter reader, IMHO, could be at risk if the case had short. I realise that any short so close should blow the fuse quickly enough, not like a TT situation. So am I being too cautions?
Hypothetically if this was a TT i guess it would have to be installed after the Main RCD?
Thnaks
JOhn