I would put the SPD in a metal DIN enclosure. If something goes wrong / big strike they might get very hot (though they have solder links to disconnect in that case).
If you can run the cables (25mm tri-rated?) from isolator to DIN box to board then use the sort with the double connections so they have practically no additional inductance. This is the sort I have used (TN-S style):
They also do one more like the common sore with different N-E protection for TT systems:
They are OK with 125A supply fuses for "V wiring" (Kelvin 4-ware style), not requiring any additional protection.
If you can run the cables (25mm tri-rated?) from isolator to DIN box to board then use the sort with the double connections so they have practically no additional inductance. This is the sort I have used (TN-S style):
Type 1+2 Lightning Current and Surge Arrester (KM1+2-25-4+0 SC) - Kingsmill Industries
System: Three Phase TN-S & TN-C-S/4 Pole Nominal Voltage: 230V AC
kingsmillindustries.com
They also do one more like the common sore with different N-E protection for TT systems:
Type 1+2 Lightning Current and Surge Arrester (KM1+2-25-3+1 SC) - Kingsmill Industries
System: Three Phase TT/TN-S/4 Pole Nominal Voltage: 230V AC
kingsmillindustries.com
They are OK with 125A supply fuses for "V wiring" (Kelvin 4-ware style), not requiring any additional protection.