Discuss Type B or C RCBO in the Australia area at ElectriciansForums.net

Reaction score
126
Greetings.

Friend of mine has a fridge freezer and a standing freezer that need RCBO protection.

Both these appliances run off the same socket which is a separate radial so easy to protect as it will only be these two items on this one particular circuit.

I am not sure of the starting current of these appliances and so was wondering whether to fit a type B or type C 16 Amp RCBO.

What do you think?

Thanks a lot.
 
firstly, measure the Zs of the circuit. if it's above the max. for the 16A type C, ( 1.44 ohms ) . fit a type B.
 
Never had a problem with a type B in these circumstances...as it is unlikely that both appliances will start at exactly the same moment there are not likely to be any issues.....I would fit whatever I happen to have,a Type B or C...as it is RCD protected Zs is not likely to be an issue either....1667 ohms applies..
 
Last edited by a moderator:
Never had a problem with a type B in these circumstances...as it is unlikely that both appliances will start at exactly the same moment there are not likely to be any issues.....I would fit whatever I happen to have,a Type B or C...as it is RCD protected Zs is not likely to be an issue either....1667 ohms applies..

I think it does, or at least could!! RCD protection is classed as ''Additional'' in other words ''Don't Rely on it!! RCDs can and often DO fail!! Then your Zs becomes very important, very fast!! lol!!
 
Greetings.

Friend of mine has a fridge freezer and a standing freezer that need RCBO protection.

Both these appliances run off the same socket which is a separate radial so easy to protect as it will only be these two items on this one particular circuit.

I am not sure of the starting current of these appliances and so was wondering whether to fit a type B or type C 16 Amp RCBO.

What do you think?

Thanks a lot.

Why do you think you need RCD protection?
 
I think it does, or at least could!! RCD protection is classed as ''Additional'' in other words ''Don't Rely on it!! RCDs can and often DO fail!! Then your Zs becomes very important, very fast!! lol!!

An RCD may be classed as either additional protection or to satisfy disconnection times....411.4.9.

If in the case of the OP if it was found that starting surges were a problem with a type B...and the Zs exceeded the maximum allowable for a type C OCPD would you rewire the circuit in a larger cable to bring it within the allowances for a type C..??,(or some other expensive fix?), when the regulations permit the RCD element of the device already installed to meet the requirements for disconnection times?
If you prefer the first option I'm glad I'm not one of your cutomers.
 
Last edited by a moderator:
I'd be inclined to go with glen sparks point and run in a radial but i would run it in a 4 or 6mm only reason is the cpc is larger in these so there fore the Zs readings should be lower i am a big fan of keeping the Zs as low as possible ,and for reasons eng54 has stated RCD's do fail , for certain circumstances you can install sockets without RCD protection
 
not only fail, but trip when you are away for a few days and leave you with a soggy, expensive mess of what used to be frozen food. bang it on it's own radial, no RCD and bury the drop in a length of 20mm galv. conduit ( earthed, ofd course) sssimples.
 
It's in a garage with a damp floor.
The lead sheathed TN-S cable runs right under the garage so for safety reasons I was thinking of an RCBO.

Personally I would prefer no RCD at all, the wiring is in surface clipped PVC conduit and the socket is already on its own radial but seeing as how everybody is health and safety mad these days I think it best to RCBO it.

The fuse board has a spare way which will have a 16 Amp non RCD protected MCB ready just in case the fridge freezer does trip out.

I'm really in two minds about this, maybe I will just give them a socket next to the fuse board for when they go away, they can plug their freezers into this socket whilst on holiday.

ZS is below 1 Ohm.
 
Personally I would prefer no RCD at all, the wiring is in surface clipped PVC conduit and the socket is already on its own radial but seeing as how everybody is health and safety mad these days I think it best to RCBO it

Although just labelling said sockets is allowed within the regs, if you are that bothered (sockets may be used outdoors blah blah), you could put special plugs on the appliances and change the socket outlet to match, eg. you can get plugs (and sockets) where one pin is turned through 90 degrees, so nothing else will be able to be plugged in.

And put that outlet on a non RCD side of the board.
 
Or cut plug off and wire it into a fused spur <WAITS for warranty expires if-you-do-that post....>
I heard a rumour that cutting moulded plugs off invalidates your car insurance and stunts the growth of any veggies your growing in your garden. :biggrin:
 
I heard a rumour that cutting moulded plugs off invalidates your car insurance and stunts the growth of any veggies your growing in your garden. :biggrin:


what's car insurance? and we don't have plumbers or kitchen fitters growing in our garden.
 
An RCD may be classed as either additional protection or to satisfy disconnection times....411.4.9.

If in the case of the OP if it was found that starting surges were a problem with a type B...and the Zs exceeded the maximum allowable for a type C OCPD would you rewire the circuit in a larger cable to bring it within the allowances for a type C..??,(or some other expensive fix?), when the regulations permit the RCD element of the device already installed to meet the requirements for disconnection times?
If you prefer the first option I'm glad I'm not one of your cutomers.
might only need an additional cpc ....parralleled up with the existing one in the cable..........
 
I'd be inclined to go with glen sparks point and run in a radial but i would run it in a 4 or 6mm only reason is the cpc is larger in these so there fore the Zs readings should be lower i am a big fan of keeping the Zs as low as possible ,and for reasons eng54 has stated RCD's do fail , for certain circumstances you can install sockets without RCD protection
4mm??...bad cable to use nick mate as dont forget....still only a 1.5mm cpc..........
 

Reply to Type B or C RCBO in the Australia area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
746
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
290
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
For a change its nice to have a clean slate to work to. Client wants their garage rewired (and boy does it need it!) so they can have the...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock