I am going to to new circuit at customer's dwelling and best way is to to do it outside of the house but laying cable on mortar/bricks.
Can I use twin&earth cable and use trunking or only armoured cable.
Thanks
Mac
 
Don't use twin and earth, it will degrade in the sun, same reason not to use trunking. You can use SWA but this may be overkill if you're just running down a wall and the cable isn't going to be buried.

In scenarios like that I use NYY-J, commonly referred to as Hi Tough. It is suitable for external use, and comes in a variety of sizes and no. of cores. And is much easier to deal with than SWA for this kind of job.

Fix it to the wall with SWA cleats, jobs a good 'un.
 
Hi.
I am going to to new circuit at customer's dwelling and best way is to to do it outside of the house but laying cable on mortar/bricks.
Can I use twin&earth cable and use trunking or only armoured cable.
Thanks
Mac
Where does the cable originate and what is it feeding ?
 
What about mechanical protection?

As @Gavin John Hyde says, it's tough stuff, but you have to use your loaf and only use it where appropriate. I might not put it low down behind bushes for example where someone might swing a spade, and I'd probably not use it down the side of a house where a car might get parked just in case, so use the same consideration you give any cable placement.
 
Most of us would think that . It is part of the journey.
Yeah…..'laying on bricks and mortar' got me thinking, too.

Hi tuff is good stuff and handy. Just used some for lighting in a new store building. It depends on the protection required, though.
 
As @Gavin John Hyde says, it's tough stuff, but you have to use your loaf and only use it where appropriate. I might not put it low down behind bushes for example where someone might swing a spade, and I'd probably not use it down the side of a house where a car might get parked just in case, so use the same consideration you give any cable placement.
Really? How bad is your driving then, bloody women drivers ;)
 
You are all talkative :)
Thanks for your ideas, especially NYY cable, as it is something new to me.
By the way I strugle to find it at CEF or Screwfix.

Anyway, project is not going forward, as customer expect me to do it for tenner maybe two :)
Tell me guys what sort of quote you would do.
1.change consumer unit (testing + cert. obviously)
2. Add new circuit for boiler - that was that, outbuilding cable for around 8 m.
There is no spur fuse serving boiler now, and he is using extension lead ! He dont dont want to interfere with inside decoration - fancy bricks like wall (made from gypsum or so.
3. Fit and connect Nest thermostat and setup.
4. Add external socket

I expect to be a mess with rings etc as it looks like no electrian did cabling when they were refurbishing home.

I mean labour only.
How much?
 
You are all talkative :)
Thanks for your ideas, especially NYY cable, as it is something new to me.
By the way I strugle to find it at CEF or Screwfix.

Anyway, project is not going forward, as customer expect me to do it for tenner maybe two :)
Tell me guys what sort of quote you would do.
1.change consumer unit (testing + cert. obviously)
2. Add new circuit for boiler - that was that, outbuilding cable for around 8 m.
There is no spur fuse serving boiler now, and he is using extension lead ! He dont dont want to interfere with inside decoration - fancy bricks like wall (made from gypsum or so.
3. Fit and connect Nest thermostat and setup.
4. Add external socket

I expect to be a mess with rings etc as it looks like no electrian did cabling when they were refurbishing home.

I mean labour only.
How much?

My advice to you is don’t quote for Labour only
 
You can get NYY cable from TLC Direct (they have branches all over the place but do deliver as well)... other on-line retailers are available :)

For what you've described, I'd be looking at a couple of days, maybe more depending on what your pre-consumer unit change checks reveal.

If the customer wants to supply everything, make sure in your quote that you make it clear you're not liable for delays caused by incorrectly purchased items and that your time will be charged for. Also make it clear that you'll charge them if they ask you to deal with warranty issues as you're not supplying the goods.
 
Used loads of NYYJ on external ligting install for a new shopping complex. Installed on tray and the tray was lidded. A right pain to strip when the weather is cold. A jokari tool is very useful for this stuff.

Aye ..... the Jokari JOK30900 is a 'must-have' tool.

 

Reply to Type of cable to outbuilding but on bricks. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Since the deco needs doing to this property. My sister needs the TV putting on thr wall but wants the cables hiding. What will be the best way...
Replies
4
Views
397
Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Replies
8
Views
368
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
637
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
902
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top