Discuss Underfloor Heating problem in the UK Electrical Forum area at ElectriciansForums.net

B

BMW

I have a problem with some underfloor heating can anyone help? Was called to a job as the underfloor heating had stopped. It appears the controller is showing the temp as 33.2 degrees and will not move down to bring the heating on. The controller upper limit is 35 degree when you set it to this it comes on but, soon switches off as it thinks it has reached the correct temp. The controller has a indicator to say if the probe is faulty and it's not lit. It's under guarantee but the company will not send anything out until I can confirm what's at fault. Don't have much experience of these but think it's either the probe or controller. I can test the probe however don't have any paper work so don't know what the Resistance should be.
Has anyone any suggestions?

Cheers

Read more: View Profile: BMW - Electricians Forum | Electrical Advice Forum | An electrical forum for electricians in the UK | Electricians Forum
 
If the controller is telling you that the probe is faulty the manufacturer should recognise this surely?

Taking the floor up could be a nightmare to get at the probe.
 
If the controller is telling you that the probe is faulty the manufacturer should recognise this surely?

Taking the floor up could be a nightmare to get at the probe.

You do not need to pull the floor to replace the thermostat because is on flexi conduit is easy to pull it out ,but the problem I think is that the thermostat tip must be just under the heating element .
Pull it a couple inches and try again.
 
You do not need to pull the floor to replace the thermostat because is on flexi conduit is easy to pull it out ,but the problem I think is that the thermostat tip must be just under the heating element .
Pull it a couple inches and try again.

If this is the case it would never have worked properly, and the tip of the probe should be beyond the end of the flexi conduit shouldn't it?
 
ImageUploadedByTapatalk1356036364.842695.jpg

Hopefully attached is a photo of typical readings of a probe, I think the info was from heatmat, but not too sure now.
Hope this helps
 
Did you check the resistance of the matt? Does the client know what rating and size the matt is?

Sounds to me that you need to demonstrate that the matt is or should work and then send the controller back. They may want to invoice you for the new one so pass this cost on to the client, or better still get them to arrange it.
 
Many thanks for all your comments. just one point the indicator on the controller did not light so it thinks the probe is ok. I think SYkraps got it the wrong way round which makes me think it's the controller?
 
That's great just one thing I dont know what the temp is as its not working. Controller showing 32 degree but as it's been off day's that cannot be right. Do I use the general room temp?

Bruce
 
If this is the case it would never have worked properly, and the tip of the probe should be beyond the end of the flexi conduit shouldn't it?

No .The tip of the probe should be inside the flexi conduit so its easy to chainge and the end of the flexi conduit should be blocked with tape to stop the tile adhesive to get inside .
 

Reply to Underfloor Heating problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hi, this is a bit complicated. We installed two separate underfloor heating system in our downstairs area. One at 240V and according to the...
Replies
3
Views
973
Hi people, I’m new to the forum, first post so here goes. I’m wiring a heating control system and at the moment the customer wants as follows; A...
Replies
0
Views
845
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock