Discuss Underground cable Question. in the UK Electrical Forum area at ElectriciansForums.net

GBDamo

-
Esteemed
Arms
Reaction score
3,010
Hi All,

To me 522.8.10 is quite clear, armoured or the like (concentric) underground unless in a conduit that offers protection equal to that of armoured.

However just had a scouse wide boy "electrician" come back from a job with the armoured cable and glands he'd been sent with..."didn't need them mate"

I know the cable has gone underground and I know he has used T&E run in PVC conduit.

Is there any way that this could be considered compliant....ever..even the most tenuous link to compliance that the gobshite could come out with?

Thanks
 
Well for direct burial swa is the way to go however a twin and earth cable installed in a material such as polypropylene or similar material ducting ,giving adequate mechanical protection is acceptable.
 
Well for direct burial swa is the way to go however a twin and earth cable installed in a material such as polypropylene or similar material ducting ,giving adequate mechanical protection is acceptable.
Can someone point me to where I can get this plastic ducting that gives equivalent mechanical protection as SWA?

Seriously is there a manufacturer that certify a product as giving mechanical protection equal to that of SWA?
 
A cable in a duct should be buried at a suitable depth say 600mm and marked by means such as marker tape or cable tiles all should give adequate mechanical protection.
Bs en 61386-24 is the Standard for underground conduits.
 

Reply to Underground cable Question. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
691
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
907
As the title says, I wonder if anyone has any knowledge of specialists firm who run in armoured cables underground? I have a 250m run of two...
Replies
11
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
835
So I'm an extremely well seasoned electrician - and pretty much thought I could do a workmanlike job of the majority of skills expected ...
Replies
6
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock