Discuss Underground HV cable & Communication separation distance in the UK Electrical Forum area at ElectriciansForums.net

L

laxmi

Hi,
Is anyone can suggest me, what is the separation distance between underground HV cable and Communication cable? An existing communication duct is found across the new HV cable route whilst new trench is dug for HV cable laying. Is there any reference or literature that mention about the separation distance?
Regards,
 
528.2 Proximity of communications cables


In the event of crossing or proximity of underground telecommunication cables and underground power cables, a

minimum clearance of 100 mm shall be maintained, or the requirements according to (i) or (ii) shall be fulfilled:

(i) A fire-retardant partition shall be provided between the cables, e.g. bricks, cable protecting caps (clay,

concrete), shaped blocks (concrete), protective cable conduit or troughs made of fire-retardant materials

(ii) For crossings, mechanical protection between the cables shall be provided, e.g. cable conduit, concrete

cable protecting caps or shaped blocks.

NOTE 1: Special considerations of electrical interference, both electromagnetic and electrostatic, may apply to telecommunication


circuits, data transfer circuits and the like.

NOTE 2: Segregation requirements for communications services are given in BS 6701 and BS EN 50174 series.
 
Technically, HV circuits from a HV source are outside of the scope of BS7671, but the requirements above are clearly a good place to start.
If the cable is not for a private network and will be adopted by a DNO they should be able to advise on their specific requirements.
If you search online you will find trenching/cable installation guides from some of these companies showing depths and separation of cables/services.
 
Last edited:

Reply to Underground HV cable & Communication separation distance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
900
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the...
Replies
6
Views
1K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
We have recently purchased a home in TX built in the 1920s, and the wiring is an assortment of multiple wiring events. There aren't any local...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock