Carrying out an EICR and some minor works on a client's flat.
This is a grnd floor flat in a converted victorian house.
All the services go into the lobby of the basement flat.
Water, gas and electrical meters are all there. The bonding is a bit flaky but easily rectified.
Bonding, main protective earth from the supply and to the fuseboard all connect to a MET adjacent to the meter in the basement.
There is a TN-S supply BS1361 > meter > switch fuse with 40a HRC fuse > 10mm T&E (3 metres ish above) > Wylex consumer unit (in good condition unfortunately)
Problem:
The cpc of the 10mm T&E supplying the flat is only 4mm and the MET is in the basement.
In effect the main earth conductor is 4mm but the Main protective conductors are 10mm so no matter how I try to make a case for the 4mm (haven't got all the figures i need for the adiabatic yet) it is effectively down grading the equipotential zone..
The way I understand it is that no matter what the adiabatic equation tells me I need a minimum of 10mm to maintain the equipotential zone.
Somebody please give me a straw to grasp at there's a massive concrete slab between the basement and the flat.
Thanks
Steve
This is a grnd floor flat in a converted victorian house.
All the services go into the lobby of the basement flat.
Water, gas and electrical meters are all there. The bonding is a bit flaky but easily rectified.
Bonding, main protective earth from the supply and to the fuseboard all connect to a MET adjacent to the meter in the basement.
There is a TN-S supply BS1361 > meter > switch fuse with 40a HRC fuse > 10mm T&E (3 metres ish above) > Wylex consumer unit (in good condition unfortunately)
Problem:
The cpc of the 10mm T&E supplying the flat is only 4mm and the MET is in the basement.
In effect the main earth conductor is 4mm but the Main protective conductors are 10mm so no matter how I try to make a case for the 4mm (haven't got all the figures i need for the adiabatic yet) it is effectively down grading the equipotential zone..
The way I understand it is that no matter what the adiabatic equation tells me I need a minimum of 10mm to maintain the equipotential zone.
Somebody please give me a straw to grasp at there's a massive concrete slab between the basement and the flat.
Thanks