I thought that alsoInteresting that the inspection schedules tick everything Coded as satisfactory.
It was the 60kVA demand that I noticed - 260ish Amps!I thought that also
He has
3.7 ticked but there is no effective water bond
4.4 is ticked- yet plastic consumer unit (C3 if OK and no signs of thermal damage)
4.10 is ticked did he add a 6 monthly notice?
4.19 is ticked yet RCD's are present on one circuit in the consumer unit
5.2 is ticked (does he have x ray vision to see all the cable routes below floors / behind walls?)
5.12.1 -5.12.3- he has picked this as a C2 yet has ticked it as satisfactory outcome ???
5.12.5 - bathroom lights not RCD protected but ticked to say OK
Pretty poor standard of EICR report (still an unsatisfactory IMO)