Search the forum,

Discuss unusual electrical faults in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

There seems to a fault on here that happens alot.

Its the "I went to look at a RCD/MCB/RCBO keeps tripping fault, what could be causing it?" Without actually dong any testing and then thinkng we can solve it for them fault.
 
10 o'clock every Sunday in a pub the RCD used to trip no other time just 10 o'clock ,go to the RCD reset no problems till the following sunday after 8 weeks of it just tripping the once i was called out to it and found it was a damaged cable where a rat had nibbled the insulation and drips from the beer tap dropped onto it, why just 10 o'clock on a sunday ill never know.
 
I had one of them every day at eight pm the house would trip got there tester all ok in the end it was a time clock but it went passed the fault so it was always clear
 
Had an alarm that went off at 4pm every day,the lad that fitted it had run one of the cables alongside the cable from roomstat and heating fired up at 4 pm.This caused an induced into the alarm cable and set it off.
 
Had a room dedicated to a UPS. it had an A/C installed as well as an emergency stop by the door (50v) every time every time the compressor kicked in out would go the UPS took us some time to find the problem, compressor kicked in induced a voltage into the stop circuit switched off the UPS twisted screened pair soon sorted that little issue out
 
There seems to a fault on here that happens alot.

Its the "I went to look at a RCD/MCB/RCBO keeps tripping fault, what could be causing it?" Without actually dong any testing and then thinkng we can solve it for them fault.
Remember JRC and his wet leaves problem?
A particular favourite of mine
 
smoke detector bleeping on a new build ive taken the head out and the battery and the base was bleeping said the customer ..................... smoke detector in a cupboard that was bleeping with flat battery
 
had a few call-outs to intruder alarms that i had installed. customers complained it was bleeping. each case was a smoke located close to the alarm panel.
 
Called to a recently rewired property a couple of weeks back, no certs and installer now no longer answering calls.
Gas fire with a back light in it but the back light now doesn't work, until you turn the thermostat up.
The couple paid £3k for the rewire, I'll be taking a dig into it soon. I think it's safe to assume there'll be one or two remeds.
 
Extractor fan 'stays on constantly'. Got there at 7.30pm after long day and received 'frosty reception' as it was obviously something that we had royally f'd up. Should have seen the look on their faces when I pulled the (previously demonstrated) chord!!
 
Extractor fan 'stays on constantly'. Got there at 7.30pm after long day and received 'frosty reception' as it was obviously something that we had royally f'd up. Should have seen the look on their faces when I pulled the (previously demonstrated) chord!!
A minor or E#sus4?
:)
 
Built in fridge isn't working.

Genuine call out about 3weeks ago - the cheeky 'bread bin' had obviouslly been knocked and turned the fuse-spur for the fridge on the worktop off behind it.

Customer was red-faced, i had a chuckle and everyone lived happily ever after.
 
cooker stopped working.

eventually tracked it down to customer hanging a picture over the isolator and the picture switching the switch.

customer had no idea what the switch was for, had never used it and assumed it was no longer used.

in fairness it was on a diferent wall to the cooker.
 
Built in fridge isn't working.

Genuine call out about 3weeks ago - the cheeky 'bread bin' had obviouslly been knocked and turned the fuse-spur for the fridge on the worktop off behind it.

Customer was red-faced, i had a chuckle and everyone lived happily ever after.
and you charged them an hour for wasting your time yeah?
 
Must have been high up then this isolater

Yes it was. It was in a ridiculous place for a cooker switch TBH.

The conversation went something like ..

Where is the switch?

There isn't one.

Have you done anything just before it stopped working?

Just hang this picture.

Remove picture, switch on, re-hang picture, laugh, finish coffee and drive home.
 
Went with Camerabloke to look at a faulty alarm the other day, door opens come in the box is in there, so he proceeds to pick up all the clutter in the cupboard, bung it on the Kitchen floor, Camerabloke does the biz and matey chucks all the stuff back in the cupboard, some people?
 
Had one that took around a month to solve, with approx 6 visits in total. RCD was tripping intermittently only on hot and sunny days and in the late afternoon only. Straight away I was thinking WTF! Long story short it turned out to be a cable to an outside light that went through the wall between the brick and a dark coloured uPVC door/window frame. The frame was heating up and expanding just enough to slightly crush the cable. Only found it after the umpteenth visit and the customer mentioning their uPVC door did not open at all after a hot sunny day, which made me think was this related.

I hate intermittent faults - PITA usually.
 
Strangest one I was ever involved with went something like this:

Company had shut down for a week so we had all the HV testing done, After the testing and all the HV was back up and running my then boss was turning all the LV sub main breakers back on when one blew up when he turned it on!
Give him a nasty burn on his arm and the air turned blue.
So anyways contractor was called to test it and replace which they did, IR testing clear and breaker replaced turned on and it trips instantly (luckily no boom this time).
So they re-checked everything again and said it was ok and couldnt understand it.
So My gaffa concludes this is BS and wants a second opinion so sends us in to break the circuit down and test.

This perticular breaker fed a sub main board which had the breakers for 2 DB's and 2 Lifts which were all isolated so we knew the fault was between the sub station and the sub board.

So we stripped the sub board down to basics, IR tested the bus bars etc etc and found nothing!

I ring the gaffa and tell him its all clear and we found nothing, He shouts and swears at me that there has to be somthing (which I agree) But nether the less there is nothing.

By this time we are all getting a bit ****ed with this thing so in a bit of a temper I smack the side of the board and low and behold a 32mm metal hole saw cut out bounces onto the floor and you would never guess it was all black and crispy!

I have no idea how it didnt show up on the IR tests or where it was actually hidden, I can only assume the second time the circuit was energised it had blown off to a location undisclosed until I smacked the board one!

But after putting everything back together and turning the breakers back on everything was fine and dandy again :)
 
Last edited:

Reply to unusual electrical faults in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
821
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
684
Hi all, I have an unusual issue with a recent rewire I have just completed which I hope you guys can assist with. For background, this is a...
Replies
19
Views
2K
Experienced DIYer, rewired two houses (and certified by qualified electrician) way back in the day when you could do that. Electronics I'm...
Replies
3
Views
375
Hi All, I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock