Search the forum,

Discuss Using 400v transformer pair to avoid cable runs... in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
127
I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heatpump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?
 
Well in theory it may just work, after all HV transmission works on very similar principles, higher voltage transporting less current.

I have to admit that I have never personally done anything like this, and well I suppose there is more than one way to skin a cat. I would love to see some figures on this
 
I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heatpump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?


Yes but not in a bloody garden!

Before you go any further concider the cost of two transformers as against the correct cable. Then you will have the earthing of the secondary output of the remote transformer to contend with. Current inrush will be a problem with two transformers. Finaly to use the exsisting cable i would be looking at 660V.

Has the client got deep pockets? If he has tell im to employ a landscape gardener to repair the damage done putting the correct cable in.
 
Sorry got my numbers wrong, it's a 12kw output HP (allow 3.5-4kW input) + the pool pump/filter 500-800w so the demand is only say 5kW...

That makes more sense...
 
if you are going to that trouble why not go all the way and step up to 11kv that should counteract any losses in the cable,if you can get them use transformers with on load tap changers that way you can adjust to compensate for any difference in voltage outside your needs.
 
I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heat pump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?


Not to boost the CCC of a tiny 1.5mm SWA cable i haven't!! lol!! The cable was too small when it was first installed, for the type of distances your talking about. I take it there is a good few metres to add to that 50m either side of this playground?? Is this installation for a school of some sort??
 
Not to boost the CCC of a tiny 1.5mm SWA cable i haven't!! lol!! The cable was too small when it was first installed, for the type of distances your talking about. I take it there is a good few metres to add to that 50m either side of this playground?? Is this installation for a school of some sort??
Well mate you,ve disappointed me!we are all taking the mick in a roundabout way and then you come on and don,t even mention earthing.how disapointing lol.
 

Reply to Using 400v transformer pair to avoid cable runs... in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock