Discuss Very high r1+r2 readings and Zs in conduit? in the UK Electrical Forum area at ElectriciansForums.net

K

Kev2632

Hi,

Why would I be getting very high r1r2 readings and Zs readings in a water heater circuit wired in the existing conduit when the house was built back in 19oatcake...? Would the conduit have anything to do with it and if so? Why?

Thanks
 
Not enough info to make a judgment Kev. What's the earthing system/Ze/Zs readings on other circuits/have you recently installed an RCD etc etc etc
 
All my other circuits readings was good, tn-s system, all connections are tight, and disconnected the water heater supply side from the switch and was still getting weird readings??
 
A jb could be under a floor, if the conduit is your CPC then a poor loint could be to blame but like Voltz said, I'm clutching a little here
 
kev,
sounds like you have a break in the conduit joint ive had similair problem before in a church :smoking: make sure you completely eliminate the swith from the circuit too
 
Yea that's what I'm thinking too, yea I elminated the switch from the circuit so I only had my live coming in from the consumer unit, and tested to the earth on the backpack where the conduit came in, you know?
 
with the CSA of the conduit in which its wired, will that allow it too have such a high reading? or would that normally give a very low reading if the conduit is " sound", because the CSA area is bigger so it should in theory have alot lower reading than the R1+R2 of live to earth in twin and earth yea??
 

Reply to Very high r1+r2 readings and Zs in conduit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
588
I’ve just changed a few lights for a customer and I rarely do testing so not very knowledgeable on it. I tested 3 lighting circuits. 1st circuit -...
Replies
7
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock